The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
Yesterday at 09:09 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 175 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#199547 - 03/01/11 09:14 AM Multiple Branch Feeders to the same building
kitha Offline

Registered: 11/12/02
Posts: 10
Loc: Hamilton, ON, Canada
I have the service entrance panel in one building(say bldg#1) and it feeds to an existing building(bldg#2) with a 400A underground feeder. An additon is required to the building#2. Due to that total service required is 600A. Can I add a second 200A underground feeder to building#2 while the previous 400A underground feeder is stil there? This is for Ontario Canada. Do not mixup with Rule6-102 whic is applicable for multiple utility services. In my case utility meter is in bldg#1. No more utility meters are required for bldg#2.

2014 / 2011 NEC & Related Books and Study Guides
#199554 - 03/01/11 11:46 AM Re: Multiple Branch Feeders to the same building [Re: kitha]
mikesh Offline

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
The answer lies in part with the utility if the second building is metered by them. BC Hydro does not like 2 meters for the same customer space.
If not the Ontario Authority might require demarking the area the other feeder supplies. Nothing worse than cross wiring a place from 2 panels.

Is the addition part of the same occupancy? If so maybe dedicating the new 200 to the addition.

I can't think of a code rule that prevents what you are planning. Certainly the need to disconnect the entire building in a fire might need to be addressed and lableing could be very important IE a sign at each panel stating there is another panel and at the supply end too.

#199641 - 03/03/11 08:55 AM Re: Multiple Branch Feeders to the same building [Re: kitha]
jay8 Offline

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
if this is a 208 volt feeder you could consider retaining single feeder and stepping up to 600 volt at building 1 and back down to 208 at building 2, which would give you the capacity. But if the feeder is already 600 volts, then I guess its back to second feeder.