The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Trumpy
01/20/17 06:20 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 20
Ruben Rocha 17
Trumpy 15
gfretwell 15
Who's Online
2 registered (Admin, Trumpy), 34 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#199254 - 02/17/11 06:48 PM Thought experiment with xfmrs and lamps
LarryC Offline
Member

Registered: 07/05/04
Posts: 782
Loc: Winchester, NH, US
Thought experiment:

Three single phase pole mount transformers 4160/240 CT

High voltage is 4160 Wye, Low votage 120/240 CT delta.

High voltage and low voltage share common neutral/earth.

Car accident isolates neutral from rest of power distribution network. The three 4160 lines are still intact, the earth connection via building bonds still intact.

Q1) If transformers are equally loaded, no shift on high voltage side. Correct?

Q2) Assuming stable transformer loading, no shift on low voltage side too?

Q3) What happens when most of 3 phase loads dissapear, leaving a significant single phase load?

Thanks

LarryC

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#199257 - 02/17/11 08:01 PM Re: Thought experiment with xfmrs and lamps [Re: LarryC]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
The line to neutral loads will balance, just like in a regular120/240. If one side is more heavily loaded, the magic smoke will be coming out of the other side. Motors on both sides are in danger.
_________________________
Greg Fretwell

Top
#199263 - 02/18/11 10:32 AM Re: Thought experiment with xfmrs and lamps [Re: gfretwell]
LarryC Offline
Member

Registered: 07/05/04
Posts: 782
Loc: Winchester, NH, US
Would the HV "neutral" shift with the unbalance and difference between this "neutral" and the rest of the power company "neutrals" in the area, result in current thru all available paths like the plumbing and the earth itself?

Top
#199264 - 02/18/11 11:41 AM Re: Thought experiment with xfmrs and lamps [Re: LarryC]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
If you are talking about losing the neutral on the line side of the pole pigs, it would really depend on where you lived. Some places have a better "ground" than others. If this was metal water piping, all the way back to the pumping station, you might not even notice the neutral was gone. If you are in Florida with plastic piping and sand around the electrodes, you are still going to balance the loads and the neutral will track that ratio. This is where you could be saved by diversity. The more customers you have on the load side of the break, the better chance you have that the loads will balance. It is still going to be pretty unstable.
_________________________
Greg Fretwell