The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 185 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#19923 - 01/05/03 05:13 PM # of outlets by the point?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
OK, I've got to confess...I was watching "This Old House" today.
They had an "electrician" that in addition to some incredibly bad work mentioned that outlets were computed by the "point", with a lighting outlet=1 point and a recp=2 points. (A certain # of points could be put on a 15A circ, 20 A circ).
Huh?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#19924 - 01/05/03 07:06 PM Re: # of outlets by the point?
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
I didn't see the show, but I'll partially defend the guy. This is probably just his way of determining circuit capacity. Almost everybody I know uses different numbers for residential. Some go strictly by X number of openings, others will look at it with some grace given to outlets that you know won't be used and don't count them. How do you determine when to cut off a circuit, and don't tell me you calculate the actual load because you have no way to know what people will use them for and residential doesn't have the same restrictions that commercial does.

[This message has been edited by Electric Eagle (edited 01-05-2003).]

Top
#19925 - 01/05/03 07:33 PM Re: # of outlets by the point?
ga.sparky56 Offline
Member

Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
Eagle do you always have a plan with the electrical on it or do you lay most of it out yourself?

Top
#19926 - 01/05/03 07:58 PM Re: # of outlets by the point?
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Usually we have to lay it out ourselves. Even if we have prints, they don't break it down by circuit, just where they want the fixtures and switches.

Top
#19927 - 01/06/03 03:26 PM Re: # of outlets by the point?
Sandro Offline
Member

Registered: 12/30/01
Posts: 449
Loc: Stoney Creek, ON, Canada
Hrm... Canadian EC states that maximum 12 receptacles on a 15A circuit. I wonder how they agreed upon that figure? 1A per receptacle? 12A = 80%

Top
#19928 - 01/06/03 04:56 PM Re: # of outlets by the point?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Electric Eagle,
No need to defend the guy. I just haven't heard of such a "system", and wondered if you guys had. (I'm not trying to ruffle any feathers)
Some of the things the guy did on the show were undefendable.

How do you resi guys determine the number and distribution of your general-use recps./lighting outlets? (will we get 5 different answers from 5 different people?)

Top
#19929 - 01/06/03 05:03 PM Re: # of outlets by the point?
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
AFCI's have some bearing in the layout here, since we are required to protect 'living areas', the definition has been 'interpeted' to death......

Top
#19930 - 01/06/03 05:12 PM Re: # of outlets by the point?
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
electure,

We generally take 13 openings per circuit. But this is loosely defined, because like I said earlier some outlets we know will get rare use and other times you know a 400 watt fixture will be on the circuit. I guess we get the 13 figure from the maximum outlets allowed on a 20 amp commercial circuit. Also if I know 20 - 60 watt fixture are going to draw .5 amps each, I have no problem putting all on one circuit.

How do you determine circuits?

Top
#19931 - 01/06/03 05:30 PM Re: # of outlets by the point?
ga.sparky56 Offline
Member

Registered: 11/24/02
Posts: 582
Loc: young harris georgia usa
Eagles method approximates ours pretty close.Does anyone else use all 12?

Top
#19932 - 01/06/03 05:57 PM Re: # of outlets by the point?
arseegee Offline
Member

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
For residential we put 8 to 10 recepts per 20A circuits. No lights on recept circuits. All lighting circuits are loaded to 1800 watts and we calculate the maximum fixture for the outlet. If its a bedroom we figure fan with 4 bulb light kit, 60 watt closet and so on.

I know we wire heavy but I picked up a contractor because his electrician had a long run of 12 with lights and recepts and when the home owner plugged in an iron the lights dimmed and flickered. That contractor spends about $150K a year with me now.

Top