The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
52 minutes 53 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#199217 - 02/16/11 05:50 PM Secondary Transformer Calculation
Up2code Offline
Member

Registered: 05/15/07
Posts: 55
Loc: Missouri
Hello All! Hope all of you have been hanging in there. Wife & I finally got internet back out here in the sticks! WooHoo! I have been asked to bid changing a Single Phase 400 Amp, 120/240V Single Phase Service over to a new Three Phase, 277/480V service, primarily for the customers new 460V pressure washers. An isolated single-phase transformer will be required for his new 120V plugs, lights, etc. Anyone know where I could find information/calculation on sizing the new KVA transformer that I will be needing? Thanks!

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#199222 - 02/16/11 06:59 PM Re: Secondary Transformer Calculation [Re: Up2code]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
What is this guy getting from the PoCo at the moment, mate?
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#199223 - 02/16/11 07:04 PM Re: Secondary Transformer Calculation [Re: Up2code]
Up2code Offline
Member

Registered: 05/15/07
Posts: 55
Loc: Missouri
120/240V Single Phase. But POCO is willing to bring 480/277V to his facility if needed.

Top
#199225 - 02/16/11 07:40 PM Re: Secondary Transformer Calculation [Re: Up2code]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
Our POCOs here require a load calculation of some detail ('ESI') for service installs/upgrades. That results in them providing a service.

Usual or common here for a comm/lite ind is 200 to 400 amp 277/480, 4 wire from a pole mounted set of pots.

Inside is a 277/480 mcb panel at either 200 or 400 amps. From there. dependent on the 120/208 volt loads, a 75 KVA xfr is set 100 amp primary, 200 amp secondary into a 42 circuit space panel.

Without any load info from you, we can only provide 'spec' info.

PS: The secondary (common here) is 120/208 volt, 3 phase, 4 wire...careful if you need 120/240 volt!
_________________________
John

Top
#199245 - 02/17/11 09:01 AM Re: Secondary Transformer Calculation [Re: Up2code]
Up2code Offline
Member

Registered: 05/15/07
Posts: 55
Loc: Missouri
I thought about going with 120/208V 3 phase secondary, which would serve his plugs, lights, compressor just fine. But there are currently 2-100 Amp 120/240V, single phase disconnects, which serve 2 permanent office trailers, which have to be powered back up. So single phase secondary is a must now. Yes, POCO is requesting a Load Sheet from me before they will hook up the new 480/277/400A service. Which the size of my secondary xfr is all I'm lacking. On top of that, customer has informed me he "might" add on in 4-5 years if business is good. Thanks for info all!

Top
#199251 - 02/17/11 12:12 PM Re: Secondary Transformer Calculation [Re: Up2code]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
Up:
"2-100 Amp 120/240V, single phase disconnects, which serve 2 permanent office trailers, which have to be powered back up. So single phase secondary is a must now."

IMHO, there should be no effect on the trailers, as long as there is no 240 volt specific equipment within them.

Most (not all) HVAC that I have come upon is happy with 208 to 240 volts.

Either way...75 KVA would be my way to go.