The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 310 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#199059 - 02/12/11 07:52 AM Canada vs. USA.Parrallel runs in the same conduit
Eddy Current Offline
Member

Registered: 09/26/06
Posts: 112
Loc: Ontario,Canada
Question is for Canadian code but I'm posting here because I'm curious what the NEC says. This job is in Canada but it's for a bridge going from Canada to USA.

120/240 volt service wired using parrallel 0000 conductors all in one 3" conduit. (6 wires in one 3" conduit)

Do these wires have to be derated even though they are parrallel runs of the same circuit? What's the max amps that can be run on these?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#199061 - 02/12/11 10:11 AM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: Eddy Current]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I know of no reason why you wouldn't have to derate.
315(B)(2)(a) says

Quote:
Each current-carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor.


I get 416a per pair for THHN/THWN-2

260a for a 4/0 @ 90c x .8 (derated for 6 in the pipe) gets 208 x 2.

That does not take into account the voltage drop which might actually be the limiting factor.
_________________________
Greg Fretwell

Top
#199074 - 02/12/11 04:37 PM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: Eddy Current]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Derate in Canada, too. As with the NEC, distance is a factor.

http://www.codemath.com/cgi-bin/Run.pl?script=CecAwgRw

Neutrals don't count toward derating.

Top
#199084 - 02/12/11 09:34 PM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: Eddy Current]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Actually the neutrals don't count exception only applies to harmonic circuits.

Todays modern electronic ballasts are non-harmonic and if they are significant then the exception cannot be used.

I've seen this the most in big box retail. The spec's call for #10 going home. The strips are factory whipped with #12 & Molex. The whole load at the smart board is held down to 10 Amps per hot.

( Big box retail now uses ranks of low-voltage switches connected by BAC back to national corporate. This way HQ has over-ride control on energy use, store by store -- all controlled from a master computer program. )
_________________________
Tesla

Top
#199087 - 02/12/11 10:02 PM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: Eddy Current]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Neutrals don't count in Canada on single-phase three wire and three-phase 4 wire systems. The Canadian exception is that the neutral is included on a three phase 4 wire system if only two hots are used. I do not recall harmonics being addressed in this regard, in the Canadian code.

Top
#199091 - 02/13/11 07:09 AM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: Eddy Current]
Eddy Current Offline
Member

Registered: 09/26/06
Posts: 112
Loc: Ontario,Canada
I'm trying to upgrade to 400amps using existing wires. Canadian code says 4/0 r90 is good for 235amps. Two runs in parrallel gives you 470amp. Because there's 6 in one pipe we derate to 80% (4 not counting the neutrals still have to derate to 80%) 470 x 80% = 376

I understand derating for multiple wires/circuits in a conduit but this is one circuit split into many wires. What would the difference be if they were 3 x 500mcm wires instead of 6 4/0's. Going from 3 to 6 wires doesn't add more circuits in the pipe or heat so why derate?

Top
#199096 - 02/13/11 11:14 AM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: Eddy Current]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
To Canadian code, install a 376 amp service, and the next fuse size is 400 amps in Table 13.

I don't understand the relationship between the size and ampacity of 500 mcm and 4/0. Isn't 500 mcm more than twice the size of 4/0 and less than double the ampacity?

Top
#199098 - 02/13/11 12:16 PM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: Eddy Current]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
500 kcmil is .519 sq/in, two 4/0 is .520 sq/in. (per table 8)

If you used 310.16 you get 380a in the 75c column for the 500 kcmil and the derated ampacity for paralleled 4/0s is 416a (80% of the 90c column 520a).

Evidently Canada sees this differently. Maybe they share Gerald's disdain for 310.16 wink
_________________________
Greg Fretwell

Top
#199102 - 02/13/11 02:43 PM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: gfretwell]
Eddy Current Offline
Member

Registered: 09/26/06
Posts: 112
Loc: Ontario,Canada
Interesting. So the service conductors from the POCO are single 350MCM in a conduit. What amperage are they good for using the NEC?

CEC = 325amps R90

Top
#199103 - 02/13/11 03:05 PM Re: Canada vs. USA.Parrallel runs in the same conduit [Re: Eddy Current]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Services are usually underground or overhead. Both methods have different ampacities than conduit. Aren't they aluminum conductors from the power company?