The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
1 registered (Radar), 249 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#198912 - 02/07/11 04:48 PM Commutator Arcing!!
williams Offline
New Member

Registered: 01/11/11
Posts: 6
Loc: canada
What I have is an old Rigid Pipe Threader unit 535 series. My original problem with this was that it was tripping the breaker. After doing a few quick checks and found nothing really wrong I took the motor out to find the Stator windings had arced and had a short. Thinking this was the problem I ordered a new field, bearings, brushes and brush wires would solve this issue. After reinstalling the motor to give her a try there was some sparking going on the commutator between the brushes and then 10 seconds later a tripped breaker. Now this obviously is now pointing to the armature and com but is there any thing I can do for testing before I order a new one or at least learn something for the next time.
Thanks

Top
#198984 - 02/09/11 03:26 PM Re: Commutator Arcing!! [Re: williams]
williams Offline
New Member

Registered: 01/11/11
Posts: 6
Loc: canada
Ok here is what I have found. This motor is universal AC or DC and I am using 120 V AC. The first test I did was use a Ohm Meter to see if there was any continuity between the commutator and the shaft and was in fact open. Then I use a test lamp and applied 120v to the shaft and tested to each commutator bar to see if I would get a light and I did which means the insulation was broken down. The reason why the ohm test never worked was because it only applies 10VDC were the test light is 120VAC. I never used this test light before and it worked well.

Top
#198986 - 02/09/11 05:56 PM Re: Commutator Arcing!! [Re: williams]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Over time the two components that wear are the brushes -- which are cheap and easy to swap -- and the commutator.

Without the trick equipment most commutators can't be 'tuned up.'

A worn commutator will just ruin new brushes in short order.
_________________________
Tesla

Top
#198993 - 02/09/11 08:40 PM Re: Commutator Arcing!! [Re: williams]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
For next time, a megger is a better tool for testing a motor.

Top