The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 99 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#198802 - 02/04/11 06:50 PM minimum OCPD for wall oven
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Here is the info given in the installation instruction from the oven manufacturer.

7200W, 240V dedicated 30Amp circuit

I know the minimum is 30A OCPD with # minimum #10 conductors.

Now for the maximum i figured 40Amps OCPD according to 422.11(E)(3)
30 x 150% = 37.5Amps

Am i correct on this?
_________________________
Be kind to your neighbor, he knows where you live


Top
2014 / 2011 NEC & Related Books and Study Guides
#198810 - 02/04/11 08:03 PM Re: minimum OCPD for wall oven [Re: Niko]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Niko:
30 x 150% equates to 45 . 37.5 would equate to 125% of 30.

Math aside, some may interpert the nameplate as "30 amp max", as I read it....dedicated 30 amp circuit.
_________________________
John

Top
#198818 - 02/05/11 01:34 AM Re: minimum OCPD for wall oven [Re: Niko]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
But if one doesn't interpret the name plate as the MAX, then one can use 30 x 150% and install a maximum 45A OCPD?

Thanks
_________________________
Be kind to your neighbor, he knows where you live


Top
#198821 - 02/05/11 07:31 AM Re: minimum OCPD for wall oven [Re: Niko]
SJT Offline
Member

Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
Niko,
If I had to run a circuit to the oven, I would run #8's. If the oven draws 30 amps on full (Thanksgiving Dinner) then your wire size needs to be 8's onto a 40 amp Breaker. (4 wire)
Good Day