#198563 - 01/27/11 02:54 PM old low voltage residential lighting systems
Chris_R Offline
New Member
Registered: 12/29/10
Posts: 1
Loc: Mass/RI USA
Does anyone have experience with troubleshooting these lighting systems probably from the 60's I would imagine? Any help would be appreciated. thanks
Top
Work Gear for Electricians and the Trades
#198564 - 01/27/11 03:01 PM Re: old low voltage residential lighting systems [Re: Chris_R]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Is this the GE RR7 system?

Uses relays like this on the line side



My first guess is a switch stuck and burned out the relay coil. That is about the only thing that happens if it isn't a broken wire.
_________________________
Greg Fretwell
Top
#198567 - 01/27/11 05:01 PM Re: old low voltage residential lighting systems [Re: gfretwell]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Also google around for Touch-Plate.

IIRC they invented the concept... and last time I looked are still supporting their stuff.

We can't help you until WHICH type is known.



Edited by Tesla (01/27/11 05:01 PM)
_________________________
Tesla
Top
#198578 - 01/27/11 08:38 PM Re: old low voltage residential lighting systems [Re: Tesla]
PAteenlectrician Offline
Member
Registered: 01/06/11
Posts: 64
Loc: Cressona, Pa, U.S.A. (Schuylki...
http://www.touchplate.com/
seen it on the next street over. pita to say the least.
Top
#198585 - 01/28/11 10:26 AM Re: old low voltage residential lighting systems [Re: PAteenlectrician]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
The touch plate system uses ratcheting relays, that is to say that the same signal comes from the switch for the both on & off operations. It only requires 2 wires to control the relay. (additional wires are needed in case of a pilot light on the switch to tell when it's in the on position). The low voltage pigtails on the relay are brown & red, if I remember correctly.

GE (and Sierra) use separate signals to the relays for on & off, so requires 3 wires run to the switch. The low voltage pigtails on the relay are black, red, & blue. Blue is the common conductor, red is the on signal, and black is the off signal.

Either system uses a momentary contact switch.
Top
#199075 - 02/12/11 05:22 PM Re: old low voltage residential lighting systems [Re: Chris_R]
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
I've dealt with the Touchplate, GE & Bryant systems... I 2nd PAteenletricians feelings...
Top
#199080 - 02/12/11 08:47 PM Re: old low voltage residential lighting systems [Re: Chris_R]
PAteenlectrician Offline
Member
Registered: 01/06/11
Posts: 64
Loc: Cressona, Pa, U.S.A. (Schuylki...
Waste of wire, too. Every light needed a dedicated line up from the basement. There was a gutted fusepanel with 2 1x 10's screwed across it to housesome of them. Houses in my area are baloon framed, long and skinny, therefoe 100' runs were between the box and the back bedroom lights.
Top
#199082 - 02/12/11 09:14 PM Re: old low voltage residential lighting systems [Re: Chris_R]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Actually one can simplify wiring with Touch-Plate...

That doesn't mean that the boys did so.

Touch-Plate permits you to control every light remotely, over and over and over around the house.

My sister bought a 1962 home loaded with Touch-Plate. A prior owner ( amateur ) was in way over his head and compounded his troubles. He kept stacking up loads on the few relays that he'd not yet burnt out.

Touch-Plate's one weakness is 'hung' low voltage switches. You can only get about 35 years out of them. Then you need to buy replacements.

By using two control cabinets her house does not have endless runs of full voltage switch legs.

Beyond that, if so desired, one can shift the relays at will to 4-sq boxes all over the space and have them triggered by shorter runs. It all gets down to how the house is designed. In my sisters' house routing was highly constrained because dramatic tongue and groove lumber formed the roof. Fortunately, a massive crawl space below permitted alternate routes.

In the present day, wireless systems are eating its lunch.

_________________________
Tesla
Top
#199119 - 02/13/11 09:30 PM Re: old low voltage residential lighting systems [Re: Chris_R]
PAteenlectrician Offline
Member
Registered: 01/06/11
Posts: 64
Loc: Cressona, Pa, U.S.A. (Schuylki...
I still like 12/3g switch loops best. smile
Top
#199122 - 02/14/11 06:19 AM Re: old low voltage residential lighting systems [Re: Chris_R]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
That picture looks like the old Remcon Relays. You would either find them at each light fixture. ( Above the drywall.) or else they would run everything into the attic.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals