The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 175 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#198507 - 01/24/11 01:25 PM Chimney as a chase.
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Hi Guys. Anyone ever use an old chimney as a chase? I have a customer who wants receptacles above their fireplace which used to be a wood burning fireplace. It is no longer used as such but instead has an insert with a 4" exhaust up the existing chimney. I actually called the inspector and told him that the chimney is no longer used for exhausting a wood burning fireplace, therefore the temp will never get hot enough to do any damage. He was ok with it being used as a chase as long as I secured and maintained a distance between my BX and the 4" exhaust.

Anyone done this before?
_________________________
Never trust an electrician with no eyebrows!!

Top
2014 / 2011 NEC & Related Books and Study Guides
#198519 - 01/25/11 06:51 AM Re: Chimney as a chase. [Re: mr_electrician]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
I've seen abandoned elevator and dumbwaiter hoistways used as chases...I don't see any real differences with your old chimney.
Securing the raceway may be a bit tricky due to the small size of the chimney, but it certainly sounds like it would work.
_________________________
Ghost307

Top
#198522 - 01/25/11 02:56 PM Re: Chimney as a chase. [Re: ghost307]
PAteenlectrician Offline
Member

Registered: 01/06/11
Posts: 69
Loc: Cressona, Pa, U.S.A. (Schuylki...
What if someone wanted their fireplace back? Just to be the devil's advocate, is a chimmney approved and listed as a chase? Is mc approved and listed for in chimmneys?

Top
#198527 - 01/25/11 09:05 PM Re: Chimney as a chase. [Re: PAteenlectrician]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
My first question would be, how old is the chimney?
Reason I ask this is that boring holes in a brick chimney could weaken the structure of the chimney itself.

I have to agree with the comment of ghost about the cable being un-supported on a vertical run, you can't merely have a cable hanging in mid-air.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#198533 - 01/25/11 09:39 PM Re: Chimney as a chase. [Re: Trumpy]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
I have other question to ask ya for the 4 inch insterst what class pipe you are seeing it ? if class A forget it it will get more than just warm engouh to get the cable get soft and can cause short circuit.

Class B is iffy question depending on how big the fireplace burner is.

Really I am not too crazy to leave it hanging loose in the chimeny area especally too close to the pipe.

Merci.
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#198534 - 01/25/11 09:41 PM Re: Chimney as a chase. [Re: Trumpy]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Originally Posted By: Trumpy
My first question would be, how old is the chimney?
Reason I ask this is that boring holes in a brick chimney could weaken the structure of the chimney itself.

I have to agree with the comment of ghost about the cable being un-supported on a vertical run, you can't merely have a cable hanging in mid-air.



#1) Structural concerns are for real. But with out a permit,a warranted consideration? (from an official stand point)

#2) Aren't all 'snaked' in old work cables 'unsupported'?
Balloon construction etc.

#3) My main concern, Personally,Is that flue liner double insulated?

3A) For the reason I can not assure 4" of clearance the whole way.

Top
#198539 - 01/26/11 07:19 AM Re: Chimney as a chase. [Re: Trumpy]
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Originally Posted By: Trumpy
My first question would be, how old is the chimney?
Reason I ask this is that boring holes in a brick chimney could weaken the structure of the chimney itself.

I have to agree with the comment of ghost about the cable being un-supported on a vertical run, you can't merely have a cable hanging in mid-air.



Regardless of age is there really a concern with structural integrity if there is a 1/2" hole drilled into it? To clarify other comments/suggestions the 4" duct going up the chimney is in a space that is about 8"wide. The BX is only loose in the chimney for about 24" and the rest is straped. If the home owner ever wanted a wood burning fireplace again I guess he would have to remove the BX and fix the holes and liners he drilled trough. Remember I did ask my local inspector if it was acceptable and he had no issues with it.

Personally I don't like it but thats what the customer wanted and it was accepted by inspection.
_________________________
Never trust an electrician with no eyebrows!!

Top
#199446 - 02/26/11 06:17 AM Re: Chimney as a chase. [Re: mr_electrician]
andrey Offline
New Member

Registered: 02/25/11
Posts: 7
Loc: canada,nb
Don't cross trades.Today you run cable in old chimney,tomorrow in old sewer line? Cut walls.If owner have to many questions call Electrical Inspector-he will help you.