#198394 - 01/20/11 10:41 AM AFCI at the first outlet
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
If the dwelling is using IMC, EMT, AC cable or RMC for the wiring method, is AFCI protection required? or the exception to 210.12 applies to the first receptacle only?

Thank you.
_________________________
Be kind to your neighbor, he knows where you live

Top
2017 / 2014 NEC & Related Books and Study Guides
#198395 - 01/20/11 11:14 AM Re: AFCI at the first outlet [Re: Niko]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The last few words sum it up.

Quote:
it shall be permitted to install a combination AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.


You still need the AFCI but you can push it out to the first outlet location.
_________________________
Greg Fretwell
Top
#198396 - 01/20/11 12:07 PM Re: AFCI at the first outlet [Re: gfretwell]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
I'm also pretty sure that they mean the first receptacle on that circuit, not the first receptacle on that conduit run.

2 circuits = 2 AFCIs.
_________________________
Ghost307
Top
#198405 - 01/20/11 07:29 PM Re: AFCI at the first outlet [Re: ghost307]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
All you have to do then is find the readily available (Ha Ha) AFCI device!!!
_________________________
John
Top
#198424 - 01/21/11 10:56 AM Re: AFCI at the first outlet [Re: HotLine1]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
John,

Has anyone seen an AFCI device? Tooth Fairy? Easter Bunny? ELVIS?


Top
#198426 - 01/21/11 12:14 PM Re: AFCI at the first outlet [Re: harold endean]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
...and what were they smoking when they saw it??

LOL
_________________________
Ghost307
Top
#198430 - 01/21/11 01:27 PM Re: AFCI at the first outlet [Re: ghost307]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I see Elvis at the 7-11 all the time and he has lost weight but, alas, no AFCI device.
_________________________
Greg Fretwell
Top
#198551 - 01/26/11 07:47 PM Re: AFCI at the first outlet [Re: gfretwell]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
AFCI devices are in the latest edition of EC Mag.
_________________________
Tesla
Top
#198559 - 01/27/11 09:11 AM Re: AFCI at the first outlet [Re: Tesla]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Tesla,

I am a little behind in my reading. I have 3 EC mag and 4 IAEI mags ahead of the new EC magazine. However I will get there, sooner or later! smile
Top
#198583 - 01/28/11 07:36 AM Re: AFCI at the first outlet [Re: harold endean]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Tesla:

You said...."AFCI devices are in the latest edition of EC Mag."

IF you mean page 75 of the 1-11 issue....that is the reference materials from the NEC changes/Handbook!

IMHO, and that of many others here....it does NOT exist!


_________________________
John
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 05/03/03
Posts: 1137
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 81 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals