The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 9
Webmaster 8
Who's Online
2 registered (frank, gfretwell), 363 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#198336 - 01/18/11 07:41 PM lightning protection conductor
triple Offline
Member

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
The lightning protection wire is run inside pvc through the building I am working on. However, a 50' stretch is run outside the pvc and simply strapped-up to the steel decking through the ceiling of one room. Surely this cannot be allowed? In the event of a lightning strike, couldn't the arcing and sparking created between the wire and the deck result in a fire?

Top
2014 / 2011 NEC & Related Books and Study Guides
#198340 - 01/18/11 09:41 PM Re: lightning protection conductor [Re: triple]
georgestolz Offline
Member

Registered: 06/26/05
Posts: 90
Loc: Fort Collins, CO, US
I can't think of an NEC violation, but it might run against the... NFPA 780? Whatever the lightning one is.
_________________________
-George

Top
#198347 - 01/19/11 06:40 AM Re: lightning protection conductor [Re: georgestolz]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6824
Loc: Brick, NJ USA
Lightning protection here (NJ) are installed by "Certified Installers" to the best of my knowledge. As an EC, the sites that I worked on (Country Clubs) had a lightning contractor.

What you described does not sound 'right', but that's just a off the cuff comment. All the conductors that I have noticed were routed on the exteriors of the structures.
_________________________
John

Top
#198505 - 01/24/11 10:27 AM Re: lightning protection conductor [Re: HotLine1]
sabrown Offline
Member

Registered: 12/12/02
Posts: 298
Loc: Ogden, Utah, USA
Just some items to be aware of besides the certified installer.

There is no typical requirement stating that the "down conductors" not allowed being run through the interior of a building. That being said, it does create alot more bonding issues that must be taken care of (flashovers).

There is no normal installation "shall" requirement that the conductors be in conduit.

But simply strapping a down conductor to steel decking does not meet bonding requirements assuming strapping means something to just hold the condutors in place (every 36" maximum). These are typically bonded via bonding plates or cadwelded. Whatever is used it is listed for lightning protection and has very specific requirements.

There are however requirements for regular yearly inspection of the system.

I am sorry that I can't put more information into this reply, but that would involve teaching a course on lightning protection.