#198335 - 01/18/11 07:12 PM working space
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
Does a 1/2" copper condensate line mounted to the floor 3'3" back from the front of a 277/480V VFD violate condition 2 in table 110.26(A)(1)? This pipe (grounded part) is something that could get stepped on but not backed-into like a steel railing or concrete wall so why should it be seen any different than the concrete an electrician would be standing on? If it is a violation then apparently a ridge or step in the concrete floor (even one only a fraction of an inch high) at 3'3" back would also be against the NEC.
Top
2017 / 2014 NEC & Related Books and Study Guides
#198855 - 02/05/11 08:44 PM Re: working space [Re: triple]
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
Triple,
The 3'3" is close to the 3'6" needed to satisfy the code. If the AHJ is saying it is in violation, could the condensate pipe be moved back, to keep peace?
SJT
Top
#198890 - 02/07/11 06:38 AM Re: working space [Re: triple]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
You could have them encase the cooper line in concrete but that might be a little too severe.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals