The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 257 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#198335 - 01/18/11 07:12 PM working space
triple Offline

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
Does a 1/2" copper condensate line mounted to the floor 3'3" back from the front of a 277/480V VFD violate condition 2 in table 110.26(A)(1)? This pipe (grounded part) is something that could get stepped on but not backed-into like a steel railing or concrete wall so why should it be seen any different than the concrete an electrician would be standing on? If it is a violation then apparently a ridge or step in the concrete floor (even one only a fraction of an inch high) at 3'3" back would also be against the NEC.

2014 / 2011 NEC & Related Books and Study Guides
#198855 - 02/05/11 08:44 PM Re: working space [Re: triple]
SJT Offline

Registered: 07/24/02
Posts: 242
The 3'3" is close to the 3'6" needed to satisfy the code. If the AHJ is saying it is in violation, could the condensate pipe be moved back, to keep peace?

#198890 - 02/07/11 06:38 AM Re: working space [Re: triple]
harold endean Offline

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
You could have them encase the cooper line in concrete but that might be a little too severe.