#198160 - 01/13/11 05:02 PM Chicago bonding jumper color?
cpalm1 Offline
Member
Registered: 01/06/04
Posts: 62
I recently helped a friend upgrade his service in a Chicago suburb that follows Chicago code. We failed the inspection because the inspector said that the bonding jumper from the service entrance conduit to the neutral/ground bar was green and the code specifies it "shall not be green or white". Is this true? He suggested black wire with no green tape? Also the GEC to the ground rod was green and he said that was no good but he didn't write it up.


Edited by cpalm1 (01/13/11 05:04 PM)
Top
Work Gear for Electricians and the Trades
#198163 - 01/13/11 05:26 PM Re: Chicago bonding jumper color? [Re: cpalm1]
mikesh Offline
Member
Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Only in Chicago.
I wonder what that is all about? What color is Bare?
Top
#198166 - 01/13/11 05:48 PM Re: Chicago bonding jumper color? [Re: mikesh]
wa2ise Offline
Member
Registered: 11/29/02
Posts: 773
Loc: Oradell NJ USA
Originally Posted By mikesh
Only in Chicago.
... What color is Bare?


Copper color? laugh
Top
#198168 - 01/13/11 06:29 PM Re: Chicago bonding jumper color? [Re: wa2ise]
cpalm1 Offline
Member
Registered: 01/06/04
Posts: 62
Originally Posted By wa2ise
Originally Posted By mikesh
Only in Chicago.
... What color is Bare?


Copper color? laugh


Which becomes green after a few years of being outside. Do I need to clean my GEC annually to prevent tarnishing if I choose a bare conductor? smile
Top
#198170 - 01/13/11 07:01 PM Re: Chicago bonding jumper color? [Re: cpalm1]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Well, it is correct that the NEC does not allow the wire from the panel to the grounding electrode to be green, or white.
Top
#198172 - 01/13/11 07:13 PM Re: Chicago bonding jumper color? [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
The only way a green color on the GEC is non-compliant is if it is a color on the insulation. 200.6 defines the colors of insulated wires.
_________________________
Greg Fretwell
Top
#198187 - 01/14/11 07:15 AM Re: Chicago bonding jumper color? [Re: gfretwell]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 897
Loc: Chicago Illinois USA
That's just one of the challenges of working in Chicago.

You never know if a requirement is actually in the Code, a specific interpretation, a leftover rule from days gone by, or just that particular Inspector having a better way to skin the cat (or having it out for you).

It would be really nice if they had to give you specific Code references when they make their comments, but that'll never happen.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 89 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals