#198140 - 01/13/11 11:48 AM Underground requirements
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
Around here for years when using a trench for burying USE cable in residential areas, it's always said that the requirement was 18", but as I read in the code it's actually 24" unless it's under a residential driveway or parking area. I'm talking about a normal run to a out building from a main panel not running under any concrete or not in conduit. Am I the only one that's been with this assumption? I've think I've even had inspectors tell me 18" before. Any thoughts on this??? Thanks...
Also when driving ground rods for a subpanel in a detached building, I'm under the assumption that it is still (2) ground rods at least 6ft. apart and attached to the grounding bar in the subpanel...???


Edited by sparkync (01/13/11 11:50 AM)
Top
2017 / 2014 NEC & Related Books and Study Guides
#198146 - 01/13/11 12:22 PM Re: Underground requirements [Re: sparkync]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
300.5 says 24" for direct burial cable/conductors unless this is a residential, single circuit, GFCI at the source end, 120v, 20a max, which can be 12"
That loophole also eliminates the need for a ground rod.

Anything else puts you into 225 part II and 250.32 along with the deeper 300.5 requirements.

They put the single residential circuit loophole in there to compromise a safer alternative to running an orange cord through the trees or along the ground.
If digging is hard there, RNC at 18" becomes a very attractive option. Personally I would go that way anyhow.
_________________________
Greg Fretwell
Top
#198182 - 01/14/11 12:41 AM Re: Underground requirements [Re: sparkync]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
Originally Posted By sparkync
Also when driving ground rods for a subpanel in a detached building, I'm under the assumption that it is still (2) ground rods at least 6ft. apart and attached to the grounding bar in the subpanel...???


The 6' rule is valid but i don't think you need two ground rods unless the resistance of the one electrode is higher than 25 ohms.
_________________________
Be kind to your neighbor, he knows where you live

Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals