The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 298 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#197837 - 12/22/10 08:44 PM 11,500 foot run of 10/4 AWG wire??
Bigplanz Offline

Registered: 03/06/09
Posts: 72
Loc: Louisville, Kentucky
I must be missing something, but I've never heard of a two mile run of 10 gauge wire. A lot went wrong with this install, but two miles of 10 gauge wire?!?!? Help me out here, am I reading this right?

The report mentions that line voltage was maintained with transformers, but what I have never heard of was that long of a run, in re: resistance.

"In order to maintain line voltage, two Acme Electrical Corporation boosting transformers were inserted in the circuit at six separate locations. Placement was determined by the drop in line voltage from 480 VAC down to 440 VAC, phase to phase."

Is this unusual in an industrial setting?

Mining accident report

Edited by Bigplanz (12/22/10 08:50 PM)
Edit Reason: clarify question, add info.

Arc Flash PPE Clothing, LOTO & Insulated Tools
#197844 - 12/23/10 07:20 AM Re: 11,500 foot run of 10/4 AWG wire?? [Re: Bigplanz]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
It's not an industrial setting - it's a mining operation. Mining operates under a different set of rules. I don't know them, so I can't comment

From my 'gut feeling,' 60 amps seems a lot for #10, and I never have liked 480 or 240v "two hots" circuits.

Oddly enough, the GEMS data would have revealed this problem- at the end of the line, a direct short to the ground wire would not draw enough power to trip the breaker. I'll bet the lights weren't working that well.