The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#197525 - 12/04/10 12:45 PM 702 Optional Standby Systems
KJay Offline

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Another thread got me wondering about this.
702.3 says, except as modified by this article, all applicable articles of this code shall apply.
So, would this negate using a GenTran style transfer panel for emergency power of circuits that are AFCI protected, since this would seem to bypass this protection when transferred to generator power?
This would also seem to be the same situation for circuits normally protected by a GFCI circuit breaker.

2014 / 2011 NEC & Related Books and Study Guides
#197537 - 12/05/10 06:52 AM Re: 702 Optional Standby Systems [Re: KJay]
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
IMO, if you put those circuits on the Gen Tran panel, then you would be bypassing the required protection and that would be a code violation. Two ways to avoid this that I can think of for an existing wiring system, install a transfer switch ahead of the panelboard or use the InterLockKit system.
Few things are harder to put up with than the annoyance of a good example.

#197540 - 12/05/10 09:45 AM Re: 702 Optional Standby Systems [Re: Tom]
KJay Offline

Registered: 11/27/07
Posts: 763
Loc: MA, USA
I think so as well. I've never actually heard any mention of this situation before, but I'm sure it's probably been dealt with previously by others.