The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 9
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 8 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#197282 - 11/18/10 12:44 AM Transformer protection
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
My existing condition:
45KVA 480V primary with 60A fused protection and 208/120 secondary with 125A CB protection

maximum load that i measured on secondary:
A= 78Amps
B= 64Amps
C= 64Amps

Under these conditions the 125Amp breaker has tripped twice. my first question why would the 125A trip? worn out/Tired breaker?

if i am interpreting table 450.3B correctly, i can install a secondary OCPD 160A that is at maximum 125% of the transformer secondary rated current? Am i correct?
_________________________
Be kind to your neighbor, he knows where you live


Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#197285 - 11/18/10 05:48 AM Re: Transformer protection [Re: Niko]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Actually since 160 is not a standard OCPD size you are permitted to use a 175 amp breaker. However, you must protect the secondary conductors at or below their rated ampacity, so changing the secondary breaker may also require you to change the secondary conductors.

As far as why it is tripping there could be some type of intermittent load that is high enough to cause the breaker to trip. Maybe an intermittent fault. Or if could be a bad breaker.
_________________________
Don(resqcapt19)

Top
#197287 - 11/18/10 07:15 AM Re: Transformer protection [Re: Niko]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Originally Posted By: Niko
Under these conditions the 125Amp breaker has tripped twice. my first question why would the 125A trip? worn out/Tired breaker?


A 200A frame breaker is tested, by UL, for more than 100 operations, so it is extremely improbable that it is 'worn out'. Poor terminations/connections causing excess heating is a more likely issue.

Did the breaker trip under the same conditions:
Time of day?
Temperature in room?
Same loads turning on/off?

Top
#197290 - 11/18/10 09:08 AM Re: Transformer protection [Re: JBD]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Originally Posted By: resqcapt19
Actually since 160 is not a standard OCPD size you are permitted to use a 175 amp breaker. However, you must protect the secondary conductors at or below their rated ampacity, so changing the secondary breaker may also require you to change the secondary conductors.


Changing the secondary conductors would be very easy. So i guess i did interpret the table correctly.

Originally Posted By: JBD
Poor terminations/connections causing excess heating is a more likely issue.

Did the breaker trip under the same conditions:
Time of day?
Temperature in room?
Same loads turning on/off?

Time of the day i don't know, but the load is fairly constant throughout the day. And the temperature of the utility room i would (guess) to be around 70F.

When i was feeling for heat on the 125A breaker i noticed the upper side of the 125Amp breaker (A phase) was very hot compare to the C phase. So it could be a bad connection inside the breaker.

Thank you for your input.
_________________________
Be kind to your neighbor, he knows where you live


Top
#197295 - 11/18/10 10:28 AM Re: Transformer protection [Re: Niko]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You should think about getting a non-contact thermometer. They are pretty cheap at one of those "China outlet tool stores" like Northern or Harbor Freight. The actual temperature is not as important as the difference when you are looking for loose connections and these work great for that although the $30-$40 one I have seems pretty accurate.
You can quickly scan a panel and locate anything that is running hot with a reasonable degree of accuracy about "how hot".
_________________________
Greg Fretwell

Top
#197314 - 11/19/10 03:06 AM Re: Transformer protection [Re: gfretwell]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Conductors to the Secondary C/B follow 'tap' rules.

Hard to believe they are undersized.

Look for OVER TORQUED -- hence stripped lugs on dependent C/B...

As a foreman, I saw that again and again.

Even j-men skip the torque wrench and lay on with a will.

Hence, broken lugs -- loose connections -- hot spots -- trips.

I got to the point that I had to personally intervene, time and again. Clown after clown figures more torque is better. That they've managed to CRACK the lug -- Well, that's a secret best kept from the boss.

Just another reason I started megging everything in sight.
_________________________
Tesla

Top
#197325 - 11/19/10 09:38 PM Re: Transformer protection [Re: Tesla]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
I just purchased a thermometer (per Greg's Suggestion, Thanks Greg) and I will check for temperature on the A phase and compare it with the C side.
_________________________
Be kind to your neighbor, he knows where you live


Top
#197326 - 11/20/10 09:01 AM Re: Transformer protection [Re: Niko]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I'm with Tesla on the importance of torquing connections. Too much is as bad as too little. Even if you've stopped short of physical damage to the lug, you may have reduced the cross section of the conductor or stressed the connector to the point where thermal cycling will finish it off.

The majority of installers do not get to see the results of their work several years down the line and have no reason to believe their installation technique is a problem.

A recent experiment/study showed that about 80% of electricians and non-electricians could not tighten a connection within +/- 20% of the required value when not using a torque wrench.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#197328 - 11/20/10 01:51 PM Re: Transformer protection [Re: Tom]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
I agree with the torquing and I torque all of connections.

I will be checking for temperature today just to see the difference between the phases. However, I have purchased a replacement breaker.
_________________________
Be kind to your neighbor, he knows where you live


Top
#197330 - 11/20/10 04:23 PM Re: Transformer protection [Re: Niko]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Once you start playing with that thermometer I think you will be surprised how handy it can be.
Knowing how hot something is running can tell you a lot once you see what they run normally.