The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 263 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#197280 - 11/17/10 10:15 PM Why TT system has this requirement?
theseus Offline
Member

Registered: 02/23/08
Posts: 11
Loc: china
IEC 60364-4-41-2005

411.5 TT system
411.5.1 All exposed-conductive-parts collectively protected by the same protective device
shall be connected by the protective conductors to an earth electrode common to all those
parts. Where several protective devices are utilized in series, this requirement applies
separately to all the exposed-conductive-parts protected by each device.

What would happen if exposed-conductive-parts collectively protected by the same protective device be connected to different earth electrode?

Top
#197297 - 11/18/10 10:45 AM Re: Why TT system has this requirement? [Re: theseus]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
You will see "ground shift" between them. "Earth" is not "zero volts" and you can see differences between ground rods that are surprisingly close together. That is why we always bond all the electrodes in a system.
_________________________
Greg Fretwell

Top
#197519 - 12/03/10 07:56 PM Re: Why TT system has this requirement? [Re: gfretwell]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
Greg,
I agree with the ground shift thing.
IMO, you are wasting time and materials installing Earth Electrodes any closer than about 12' apart.

One thing I have had good results with in the past, is instead of actually driving a second electrode, is clamping some stripped heavy copper wire to the electrode and burying that copper in a long thin trench at about 2' deep, this has bought down the actual earth electrode resistance and hence increased it's current-carrying capacity under fault current conditions.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin