#197280 - 11/17/10 10:15 PM Why TT system has this requirement?
theseus Offline
Member
Registered: 02/23/08
Posts: 12
Loc: china
IEC 60364-4-41-2005

411.5 TT system
411.5.1 All exposed-conductive-parts collectively protected by the same protective device
shall be connected by the protective conductors to an earth electrode common to all those
parts. Where several protective devices are utilized in series, this requirement applies
separately to all the exposed-conductive-parts protected by each device.

What would happen if exposed-conductive-parts collectively protected by the same protective device be connected to different earth electrode?
Top
Tools for Electricians:
#197297 - 11/18/10 10:45 AM Re: Why TT system has this requirement? [Re: theseus]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
You will see "ground shift" between them. "Earth" is not "zero volts" and you can see differences between ground rods that are surprisingly close together. That is why we always bond all the electrodes in a system.
_________________________
Greg Fretwell
Top
#197519 - 12/03/10 07:56 PM Re: Why TT system has this requirement? [Re: gfretwell]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Greg,
I agree with the ground shift thing.
IMO, you are wasting time and materials installing Earth Electrodes any closer than about 12' apart.

One thing I have had good results with in the past, is instead of actually driving a second electrode, is clamping some stripped heavy copper wire to the electrode and burying that copper in a long thin trench at about 2' deep, this has bought down the actual earth electrode resistance and hence increased it's current-carrying capacity under fault current conditions.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals