The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 295 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#197272 - 11/17/10 10:32 AM Bonding eye beams to a ground ring
SJT Offline
Member

Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
When a New Bldg.(industrial)is constructed with steel eye beams, does the connection to the beams need to be above ground level (not buried). I've seen a lot of Bldgs. with the exothermic connection above the ground. Is it by Code, to have them accesible? Or can this connection be below grade?
Thanks - Good Day

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#197274 - 11/17/10 11:05 AM Re: Bonding eye beams to a ground ring [Re: SJT]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Oddly enough, this seems to be addressed in the 2011 changes. It appears that simply having the mounting bolts of the columns in the concrete is enough- and if they're tied to the rebar with ordinary tie wire, that's certainly enough.

That sadi, I've only given the changes a quick review, and have not reviewed the code in any detail - so my understanding my be incomplete.

Top
#197277 - 11/17/10 12:50 PM Re: Bonding eye beams to a ground ring [Re: renosteinke]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
SJT:
Having the GEC (earth) connection visable for the electrical inspector may be a concern. A lot of times, the footings, etc., are already backfilled before any elec inspections are called for.

Here in NJ, the Building Inspector IS required to inspect the ufer connection(s) when he does footing/foundation inspection(s).

Also, keep in mind that the electricians may not be 'on site' for the footings/foundations to install any grounding. Additionally, there may be changes in locations, or a GEC installed at a 'wrong' location.
_________________________
John

Top
#197304 - 11/18/10 02:28 PM Re: Bonding eye beams to a ground ring [Re: HotLine1]
SJT Offline
Member

Registered: 07/24/02
Posts: 242
Loc: PATCHOGUE, N.Y.
Thanks, I will check to find out exactly how the ufer ground was ran and how they picked up the eyebeams.

Top
#197306 - 11/18/10 02:53 PM Re: Bonding eye beams to a ground ring [Re: HotLine1]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Originally Posted By: HotLine1

Here in NJ, the Building Inspector IS required to inspect the ufer connection(s) when he does footing/foundation inspection(s).


My jurisdiction is same. San Francisco bay area.
_________________________
Be kind to your neighbor, he knows where you live


Top
#197313 - 11/19/10 02:58 AM Re: Bonding eye beams to a ground ring [Re: Niko]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
The last time I faced this issue I bonded to the big steel above ground.

It was no hassle, and a cheaper procedure.

Because of water bonding and gas bonding, above ground bonding was in the plans.

Jumping over a couple of feet to clamp the big steel was no effort.

I'm scratching my head trying to figure out why you'd be so interested in having this bond done underground. From my experience, it would almost always be more expensive. Only exothermic or listed trick connectors would meet Code. By comparison it's quick and cheap to 'tag' the big iron above ground - usually in the electrical room -- or right next door.

Explain it to me.
_________________________