The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#197188 - 11/14/10 06:46 AM Arc fault breakers and manual transfer switch
nrp3 Offline
Member

Registered: 10/06/07
Posts: 27
Loc: New England
I was finishing up a portable generator set up this afternoon. The problem I was having was a couple of the circuits I had were on arc faults and would trip when switching from line to gen on the transfer switch. It is a Siemens main lug panel and I am using a Reliance 10 circuit manual transfer switch. These two circuits are on opposite phases in both the panel and the transfer switch. I don't know whether it is the generator having the neutral bonded to the frame (I guess) and the panel being a sub panel fed from a meter main with the ground and neutral seperate in the panel or something to do with the arc fault having a GFCI component not having the neutral current match the hot current now not flowing through the breaker. I did the testing without turning off the meter main breaker. I ran out of time and will return next week.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#197189 - 11/14/10 08:08 AM Re: Arc fault breakers and manual transfer switch [Re: nrp3]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
That seems to be a known problem with AFCIís and generators. As I recall, GFCI cbís have also tripped on me like that at the instant of changeover. I believe it has something to do with the neutral and grounding conductors being common at different points. Once reset tough, they appeared to function normally again.
Although the neutral of the generator isnít supposed to be bonded to the frame anyway if it is being connected to the premise wiring like that, Iím not sure that removing the bonding jumper will cure the tripping, but I suppose it might.
It seems that transfer switch that also switches the neutral would be a sure cure, but I couldnít swear to that since I have never seen one used with a portable generator setup before. I always explain the need to reset the cbís to the customer as just another step that needs to be done at the time of transfer to generator power.

Top
#197211 - 11/14/10 05:45 PM Re: Arc fault breakers and manual transfer switch [Re: KJay]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1295
Loc: Alaska
Without more info, it sounds like you setup has a double bond in the system down line of the AFCI of the breakers. Check with local code first where the main bond needs to be. Make sure that there is no other neutral/ground bonds within your system. It could be built in the genset.

As for the AFCI tripping, I can't say for certain that a double bond would trip an AFCI. An AFCI and GFCI function differently. A double bond will definently trigger a GFCI but only from a second bond is down line from the divice
_________________________
"Live Awesome!" - Kevin Carosa

Top
#197226 - 11/15/10 06:15 AM Re: Arc fault breakers and manual transfer switch [Re: sparkyinak]
nrp3 Offline
Member

Registered: 10/06/07
Posts: 27
Loc: New England
The more I think about it, the more I believe I will have to change to a panel mounted transfer switch on a small subpanel. A neutral/ground bond would be before the arc fault. These breakers have been holding for weeks with various loads in the master bedroom and lighting in the halls. I think that its because the hot and neutral aren't balanced when you switch the individual switches from line to gen.

Top
#197278 - 11/17/10 06:00 PM Re: Arc fault breakers and manual transfer switch [Re: nrp3]
nrp3 Offline
Member

Registered: 10/06/07
Posts: 27
Loc: New England
I moved all the circuits I wanted over to the subpanel next to the main panel, moved the ones I didn't back to the main and added the Siemens interlock. Those arc faults that were giving me trouble, work fine now. All the current on those arc fault circuits is the same whether on the generator or utility power. Seems to have solved the problem. That interlock is a nice piece, fits well.

Top
#197291 - 11/18/10 09:21 AM Re: Arc fault breakers and manual transfer switch [Re: nrp3]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Itís been a couple of years since Iíve installed one of those little Reliance or GenTran type panels, so I'm going from memory here, but as I recall, the ungrounded side of those AFCI and GFCI cbís are completely out of the loop once you flip those switches and transfer over to generator power, effectively removing their protection from the circuit, although the circuit neutrals remain connected to the cbís.
Iím not sure how this lack of protection plays into the NEC, but it sounds like it could be another touchy issue to deal with.
I believe the cb tripping occurred the instant line power was restored, so I guess a momentary imbalance could indeed be the issue with that. Once utility power is restored and the cbís reset, they would function normally again.
Itís good you had the option to use the interlock. A lot of times the HO provides the transfer panel they picked up at the big box store, so not always an option.