The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#196917 - 11/01/10 04:02 PM Re: Knockouts
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Are you allowed to use a bonding locknuts with concentric/eccentric knockouts?

P.S. Greg, you know where I am going with this, let's see what others have to say.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#196919 - 11/01/10 04:09 PM Re: Knockouts [Re: harold endean]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I gave you my cite, lets see what everyone else has to say.
_________________________
Greg Fretwell

Top
#196931 - 11/01/10 07:26 PM Re: Knockouts [Re: harold endean]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
UL White Book seems to indicate no problem for metal outlet boxes, regardless of voltage, but then 250.97 doesn’t specifically list them as one the methods in the exceptions for bonding over 250V.

Top
#197010 - 11/04/10 09:06 PM Re: Knockouts [Re: KJay]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Raco junction boxes are rated/listed for use with 277V circuits even with concentrics.

Ditto the competition, IIRC.

The only time I face issues is with disconnects -- especially NEMA3R for RTU.

I've never been given the opportunity to install bonding locknuts. Out my way, the only ones I've seen are in Code Handbooks.

-----------

I can say from witnessing aged rooftop installations that bonding takes a beating over time. Hence, I always run a separate bonding conductor for all circuits that leave the building.

If you've never seen it, what happens to roof top EMT runs is trips and falls. Over the years various HVAC boys manage to bump what ever EMT can possibly be bumped.

As for current installations, root top EMT runs are either contract prohibited or banned by the AHJ. Only short, to the point, EMT is permitted.

BTW, old disconnects/fuse holders are scary. Generally they are too small and too often they do not keep rain or leaves out. And then the labels are all ruined. This is not the type of stuff to handle on a wet roof.
_________________________
Tesla

Top
#197014 - 11/05/10 06:48 AM Re: Knockouts [Re: Tesla]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
The situation I am writing about deals with a new panel installed before that main service breaker. It feeds a PV system. So the feeder to this new PV panel has no overcurrent protection. Now Would a bonding locknut be suitable for use on a panel with concentric knockouts?

Top
#197016 - 11/05/10 10:31 AM Re: Knockouts [Re: harold endean]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Harold I have modified my position. I am thinking it will be acceptable. The function of the bonding locknut is to bond the raceway and if it is made up tight against the connector lip and the concentric ring with a 250.66 sized jumper, the raceway is bonded, even if the ring breaks out completely.

For some reason I had in it my mind that the concentric locknut would loosen if the eccentric broke. I guess I should not type after midnight wink
_________________________
Greg Fretwell

Top
#197020 - 11/05/10 10:57 AM Re: Knockouts [Re: gfretwell]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Greg,

If the concentric KO pops out, the grounding would be lost. The bonded locknut will still be tight against the shoulder of the connector, but the metal to metal grounding will be missing because the KO busted loose. Right?

Top
#197021 - 11/05/10 11:15 AM Re: Knockouts [Re: harold endean]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Not if there is a jumper from the locknut to the can.
_________________________
Greg Fretwell

Top
#197028 - 11/05/10 05:33 PM Re: Knockouts [Re: gfretwell]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
BTW, it is important to acknowledge that PV systems -- as generators of power are NOT infinite busses.

Further, solid-state current saturation effects mean that the kind of peak arc power available from an infinite bus does not exist.

This is true whether you're on the DC or AC side of the inverter.
_________________________
Tesla

Top
#197031 - 11/05/10 06:44 PM Re: Knockouts [Re: Tesla]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
I thought bonding locknuts just had a screw that you tighten against the box after tightening them down. If it has lug with a bonding jumper attached, wouldn’t that be a bonding bushing?

Top
Page 1 of 2 1 2 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals