The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 9
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 133 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#196500 - 10/09/10 04:55 AM Tray Cable
michelebacocchia Offline
New Member

Registered: 08/23/10
Posts: 6
Loc: Italy
Hello!!

Could I use a Tray Cable (TC) certified CSA without the use of a cable tray in an industrial equipment?or I need to use another type of cable?

Thanks!

Top
2014 / 2011 NEC & Related Books and Study Guides
#196507 - 10/09/10 11:55 AM Re: Tray Cable [Re: michelebacocchia]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Table 19 shows TC cable as suitable for direct earth burial with protection if it's marked for that use (Table 19, Note 25).

If you run TC cable in a cable tray, you need to get from the tray to the equipment the cable serves. 12-2202(2) covers that by allowing its use in conduit where it isn't in the cable tray.

Other than that, I think you need to use different cable.