The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 258 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#196483 - 10/08/10 07:58 AM Re: Shower lights
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Stop me if we have heard this before. smile As for shower lights. If you have a shower enclosure that has a door or curtain and is about 7' tall with a shower light, we all know that you need a shower trim. Now what if there is no ceiling right above the shower, or the ceiling is say 10' or 12' above the shower base. (Or a vaulted or cathedral ceiling) Does the recess light (High hat)(HH) over the shower area need to be listed for damp location? Can you use a sloped ceiling HH over the shower area?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#196485 - 10/08/10 08:53 AM Re: Shower lights [Re: harold endean]
sabrown Offline
Member

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
I would say ask the inspector, but as you are one, that sort of kills that. It comes down to a judgement call. How open is the ceiling? Where's the fan (if it exists)? What is the use (a shower room for a high school gym may require shower trim at 15')?

There is no one size fits all answer. I am currently doing a small commercial design where the shower light is just outside the stall and I (as a designer) still feel it requires the shower trim due to location, as an inspector, I would have to pass the same design with a damp listing only.

I have seen my bathroom ceilings dripping after one of my sons have finished their shower, thus my design criteria.

Top
#196486 - 10/08/10 08:54 AM Re: Shower lights [Re: harold endean]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
I think we need to ask: just what are we trying to accomplish?

As best I can tell, when it comes to lighting in shower areas, we have three issues to address: personnel shock hazards, water spray hitting the bulb, and moisture inside the fixture. (Ironically, the advent of LED and other 'cool' lights might make that third issue a greater concern).

Personnel shock is easy: If there's any way someone can touch the fixture while showering, then we need to GFI it.

Shower trims are intended to keep water drops from hitting a hot bulb, causing it to shatte. Broken glass in a shower is not something I want to have to worry about. So, if there's any way for water spray to hit the hot bulb, we need to protect it.

Since most showers are set in something of a recess, ventilation is an issue. Water can, conceiveably, condense atop the inside of the fixture, then drip onto the hot bulb. Again, this risk is reduced by using a sealed trim.

The downside to completely sealing a fixture is that moisture that enters - and moisture WILL enter - becomes trapped. I have seen fixtures with over an inch of water that, over time, has condensed within in. More important, that moisture goes to work, causing corrosion and rust.

High ceiling? Open ceiling? Severely sloped ceiling? It's perfectly possible for a fixture to be located far enough above, or otherwise positioned, so that a shower trim is, IMO, not required. Keeping in mind my earlier comments about moisture accumulation, a shower trim might actually create a hazard.

LED's, CFL's, atc., may allow more moisture to accumulate, as they do not generate as much heat- heat that can keep the insides dry.

A final 'safety' issue is: how do you change the bulb? Remember, a shower trim blocks access to the bulb; if you can't safely set up a ladder, maybe it's best to leave the can 'open' so you can reach the bulb with a pole.

Top
#196489 - 10/08/10 11:10 AM Re: Shower lights [Re: renosteinke]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Harold:
I have not had any 'issues' with this. All I come accross are shower trims! Vaulted, high, low, ceilings; all had shower trims.

As to Reno's comment...I often scratch my head, and wonder who & how are the bulbs going to be replaced! Jokingly, I asked a few ECs if they had a maintenance contract! One HO said.."don't they last 10k hours"?
_________________________
John

Top
#196491 - 10/08/10 12:13 PM Re: Shower lights [Re: HotLine1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Replacing bulbs in vaulted ceilings is always a problem but to the point here. I think all shower trims are designed to drain so you shouldn't have that goldfish bowl effect you see in jelly jars and other luminaires exposed to water.
At any rate once you get 8' above the rim you are out of the shower area as far as requiring "damp" rated covers.

Quote:
410.10(D)... Luminaires located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations
_________________________
Greg Fretwell

Top
#196517 - 10/10/10 11:53 AM Re: Shower lights [Re: gfretwell]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
John,

As for maintaining bulbs, I was on a job years ago and the HO wanted a spot light about 30' above the ground. I asked him if he was afraid of heights. He said that he was. So I asked him who is going to change that bulb 30' up there you? or are you going to call me back to change the bulb? The fixture was then installed around 8' off the ground, near the corner of the house. smile

Top
#196518 - 10/10/10 11:57 AM Re: Shower lights [Re: harold endean]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Greg,

I can see how the 8' is above the "damp" location and spraying/splashing of water is not really an issue there. As for condensation, I don't think it will happen especially if the ceiling is in the 9-12' height. The biggest issue I see is that you really can't put a shower trim on a sloped ceiling can and make it work correctly.

Top
#196519 - 10/10/10 01:16 PM Re: Shower lights [Re: harold endean]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
The code will not require a shower trim up there, but who knows what an AHJ might want. I think the biggest "damp" issue would be a rust stain streaming down that sloped ceiling after a while. I am not sure there is really a hazard tho.
_________________________
Greg Fretwell

Top
#196550 - 10/12/10 01:25 PM Re: Shower lights [Re: gfretwell]
ChicoC10 Offline
Member

Registered: 05/30/07
Posts: 169
Loc: CA
I always worry about lackluster performance most shower trims give.
If the customer can handle the slightly funky standoff of the trim I like to use a Lithonia L3 with wet trim. It's wet rated with an exposed 75W PAR30. Looks a little strange to some though. I have it in my shower, I like a bright, wake you up shower light smile

Top
#196621 - 10/17/10 12:38 AM Re: Shower lights [Re: ChicoC10]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
Originally Posted By: ChicoC10
I always worry about lackluster performance most shower trims give.
If the customer can handle the slightly funky standoff of the trim I like to use a Lithonia L3 with wet trim. It's wet rated with an exposed 75W PAR30. Looks a little strange to some though. I have it in my shower, I like a bright, wake you up shower light smile


As far for other members in here they are right on the spot and I know the last shower trim I have to deal due one ceiling is at 9 foot so I end up leave it open trim but the inspector told me make sure you use the PAR bulb not the BR rated bulbs.

Now in France that will change a bit here under 8 foot no luminaires are allowed in shower or bathtub area unless it is low voltage verison with RCD { 10ma setting instead of normal 30ma setting } but once you get above the numbers of feet/ meter of height then it will become normal set up.

Merci.
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)