The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
09/27/16 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 295 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#196468 - 10/06/10 12:56 PM Generators & Mtrs
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
150 KW 480 three phase generator.
Whats largest size mtr. it can start with cross the line starter?
Largest size mtr. with soft start.??
Largest size motor with VFD.
I;m looking for a place I can refer to for this info.
Thanks yoopersup

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#196473 - 10/06/10 03:00 PM Re: Generators & Mtrs [Re: Yoopersup]
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Not enough info provided..the real answer will depend on many variables, such as the motor's design and efficiency, and most importantly what kind of mechanical load the motor is driving.

You will need to look at it on a case-by-case basis to be sure your generator can handle the largest motor load.

And the sequence of load pick-up will make a difference.
_________________________
Stupid should be painful.

Top
#196474 - 10/06/10 03:19 PM Re: Generators & Mtrs [Re: mxslick]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Normally, the factory would supply those stats.

Is the unit asynchronous, synchronous, or synthetic wave form?

What constitutes an unacceptable voltage sag?

What is the duty rating for the alternator?

What is the duty rating for the motor?

Does it start loaded or unloaded?

What are the specs on the VFD?

These are engineering issues best resolved by the factory.
_________________________
Tesla

Top
#196476 - 10/06/10 05:16 PM Re: Generators & Mtrs [Re: Tesla]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Is there a site or Computer program all info can be put in answer come out.
I know Generator suppliers well also supply the info. Just looking for a simple way to actess
same info.

Top
#196477 - 10/06/10 05:36 PM Re: Generators & Mtrs [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
The formula is: Motor HP x KVA per HP x (1000 / (Volts x 1.73)) = LRA. Example: A 20 HP Code G motor connected to 460 Volts requires what LRA? Refer to Chart A and select 6.29 KVA/HP, from Chart A, for Code G. The formula becomes: 20 x 6.29 x (1000 / (460 x 1.73)) = 125.8 x 1.26 = 158.5 = 159 LRA. The generator must produce 159 Amps at 460 Volts, to safely start this motor. Use formula: 1.73 x Volts x Amps x .8 / 1000 for generator KW size.
Found it! heres part of it harts for mtrs. also on it.

Top