what is the closes that a receptalce can be to a remote gas pump?
Top
2017 / 2014 NEC & Related Books and Study Guides
#196386 - 09/29/10 12:44 AM Re: What Nec codes saids? [Re: peanutmydog]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Is this a "pump" or a "dispenser". The difference is the width of the class 1 div 2 area.
If this is outdoors, a safe answer is 3 feet or greater away, 18" or greater above grade ... If I am reading Table 514.3(B)(1) right. Underground raceways still need sealoffs.
_________________________
Greg Fretwell