#196382 - 09/28/10 06:28 PM What Nec codes saids?
peanutmydog Offline
New Member
Registered: 07/24/09
Posts: 2
Loc: la. usa
what is the closes that a receptalce can be to a remote gas pump?
Top
2017 / 2014 NEC & Related Books and Study Guides
#196386 - 09/29/10 12:44 AM Re: What Nec codes saids? [Re: peanutmydog]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Is this a "pump" or a "dispenser". The difference is the width of the class 1 div 2 area.
If this is outdoors, a safe answer is 3 feet or greater away, 18" or greater above grade ... If I am reading Table 514.3(B)(1) right. Underground raceways still need sealoffs.
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 102 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 10/19/00
Posts: 2724

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals