The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by geoff in UK
Today at 02:04 PM
Temporarily feeding a panel...
by Potseal
09/29/16 11:05 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 11
sparky 10
gfretwell 8
Potseal 7
Vlado 6
Who's Online
1 registered (Webmaster), 310 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#196049 - 09/07/10 01:00 AM neutral wire requirement and three ways
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
I wonder if they are going to make 12-4 NM-B more readily available for the upcoming code change to prevent generating induced voltage by someone trying to mickey mouse a three or four way.
_________________________
"Live Awesome!" - Kevin Carosa

Top
2014 / 2011 NEC & Related Books and Study Guides
#196051 - 09/07/10 10:08 AM Re: neutral wire requirement and three ways [Re: sparkyinak]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5300
Loc: Blue Collar Country
I have not encountered any problems obtaining NM with the necessary conductors. As I see it, all you need is a black, a red, a white, and a ground.

I will admit that you will need to run two cables to each switch - one 'in' and one 'out.' Again, I don't really see that as an issue with 3-way and 4-way switches; it really affects the ordinary switch, though.

Let's face it - we're going to have to get out of the practice of making the box above the fixture our "main" box. That's what the proposal changes. No more running a single cable from the fixture to the switch, and re-labeling the white wire as a switch leg. They want the feed to enter the switch, then go on to the fixture.

Good practice? Probably. Warrant becoming part of the code? I don't think so.

Top
#196058 - 09/08/10 08:49 AM Re: neutral wire requirement and three ways [Re: renosteinke]
sabrown Offline
Member

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
You already know this so to clarify, you can run to the fixture and then run a 3 conductor with ground to the switch. So this does make the switch first more likely and the likely way to run 3 and 4-ways and ending with the run to the light, otherwise the requirement for 4 conductor with ground. Just a bit more planning if you are not in a habit that already includes the neutral.

Shane

Top
#196116 - 09/14/10 01:49 AM Re: neutral wire requirement and three ways [Re: sabrown]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
If I understand it right, a grounded conductor will be required to be pulled to eash switch. In a 3 and 4 way swith loop, three wires are required to run between the switches just to switch the hot leg. How to you get your a grounded conductor to the other switches without violating 300.3(B)? Violate 300.3(B) could likey generate some CEMF and FUBAR the electronics in the switches the new rule call for.

Not only the NEC is a safety manual. Its becoming a designing manual. By bringing a grounded conductor to each switch in no way makes the wiring any safer. It's a design issue. If shhh-poopheads are using the grounding conductor as a grounded conductor, the shhh-poophead will still do what he/she is doing til someone holds him/her to their actions.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#196120 - 09/14/10 08:39 AM Re: neutral wire requirement and three ways [Re: sparkyinak]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5300
Loc: Blue Collar Country
Here's how you can do it:

Ordinary B/W/G Romex brings power to the first 3-way switch, then B/R/W/G continues to the 4-way(s), B/R/W/G to the last 3-way, then B/W/G to the lights. Between the 3-ways. you use the black and red as your 'travelers.'

What the rule eliminates - or at least makes impractical - is running simple switch legs to a junction box above the light. In effect, every switch box will need two cables to it - one 'in' and one 'out.'

I like the idea, but I don't like the rule.

Top
#196122 - 09/14/10 09:13 AM Re: neutral wire requirement and three ways [Re: renosteinke]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Another option, if you want to keep doing the "big J box at the light" method is to drop smurf tube to the switching locations.
It is not the cheapest way to go but it does give you the most flexibility later.

Down the road, I wonder how many of these "neutrals" will be hijacked as current carrying conductors for additional switches or added 3 ways.
_________________________
Greg Fretwell

Top
#196128 - 09/14/10 03:27 PM Re: neutral wire requirement and three ways [Re: gfretwell]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5300
Loc: Blue Collar Country
Someone once told me: Don't speak of it ... if it's good it runs away, if it's bad it shows up!

I just encountered a remodeling job - the guy wants to add a third switch to several 3-way light circuits. My first thought was to simply interrupt the travelers, then run a single 14-2-2 from that new j-box to the new new switch location (re-tagging the neutrals).

Well, under the 'run a neutral' rule, that short-cut is out; looks like I'll be running some more wire. Oh, Well!

Edit to add ... Since each room (for this project) has two levels of lighting, that means there will be two 4-ways at each location. Adding the neutrals and grounds means I need room in the box for 16 wires (plus pigtails, etc.) Let's face it; "switch" boxes and "stack" switches are now restricted as to your use of them.

Just run a single neutral and ground? If I was coming from a single j-box in pipe, I could do it. Since I'm using Romex, that's out - there's no form of Romex with 4 'hots,' 1 'neutral,' and 1 'ground.'

The "Law of unintended consequences" just kicked in.


Edited by renosteinke (09/14/10 03:37 PM)

Top
#196130 - 09/14/10 09:48 PM Re: neutral wire requirement and three ways [Re: renosteinke]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Push a 1/2" smurf tube down there wink
_________________________
Greg Fretwell

Top
#196131 - 09/15/10 01:13 AM Re: neutral wire requirement and three ways [Re: renosteinke]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
Originally Posted By: renosteinke
Here's how you can do it:

Ordinary B/W/G Romex brings power to the first 3-way switch, then B/R/W/G continues to the 4-way(s), B/R/W/G to the last 3-way, then B/W/G to the lights. Between the 3-ways. you use the black and red as your 'travelers.'
One of is missing something. I understand that 2011 NEC will require a grounded (neutral) wire to be pulled to every switch. 300.3(B) requires that all the wires of a circuit be ran in the same conduit, raceway, or jacket. This is to prevent CEMF. doesn't matter how you slice it, you would need a minimum of 4 wires to run a 3 and 4 way between the switches. Running 2 NM-b is a violation of 300.3(B)
_________________________
"Live Awesome!" - Kevin Carosa

Top
#196135 - 09/15/10 08:24 AM Re: neutral wire requirement and three ways [Re: sparkyinak]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5300
Loc: Blue Collar Country
B/R/W/G ... Black, red, white, ground ... that' four wires. Two travelers, your neutral and your ground. That's all you need between the 3-way switches.

Top