The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
gfretwell 13
ghost307 12
Who's Online
0 registered (), 0 Guests and 179 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#195763 - 08/20/10 02:18 PM Phase Convertor Sizing
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
MCA 74 on compressor unit (all mts taken into account).
240 v single phase to 240 v 3 phase.
40 hp convertor .
input Aprox 127 amps
outputaprox 100 amps.
Comments???
Yoopersup

Top
2017 / 2014 NEC & Related Books and Study Guides
#195777 - 08/22/10 01:10 AM Re: Phase Convertor Sizing [Re: Yoopersup]
twh Offline
Member

Registered: 03/11/04
Posts: 899
Loc: Regina, Sask.
I'm guessing you're looking at a rotary converter. Do the motors need to be de-rated? The math looks off between single phase input and 3 phase output.

Top
#195779 - 08/22/10 10:15 AM Re: Phase Convertor Sizing [Re: twh]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Any chance of doing this with VFD's? Appropriately sized VFD's can convert a single phase input to three phase.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#195780 - 08/22/10 12:18 PM Re: Phase Convertor Sizing [Re: Tom]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
This is a Full HVAC unit was ordered wrong. MCA on name plate 74 amps single point hookup.
So need about 80 amps or so on three phase side.
As starteres ect are all ready in the package looking for 3 phase power imput. Vendor told us 40 hp unit well do the trick just checking.
Yoopersup

Top