The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Trumpy
01/20/17 06:20 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 20
Ruben Rocha 17
Trumpy 15
gfretwell 15
Who's Online
2 registered (Trumpy, Admin), 29 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#195757 - 08/20/10 09:55 AM use of sealtite in damp location more than three
crselectric Offline
Member

Registered: 09/24/06
Posts: 134
Loc: albany, ca
Can I use sealtite in multi family dwelling in outside well covered area to run feeders to third floor, emt would have to be installed in 26 inch sections due to changes in floor framing at stairway decks, its passing thru storage cabinets and floors. original plan was to pass long sections up from basement, but went awry. it would be about 45 foot run, then emt in side apartment.

Top
2017 / 2014 NEC & Related Books and Study Guides
#195758 - 08/20/10 10:58 AM Re: use of sealtite in damp location more than three [Re: crselectric]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
LFMC?
Yes as long as you properly secure it and you can say it is not subject to physical damage.
You also need to pull a grounding conductor in the raceway since it is more than 6'
LFNC "carflex" has similar rules once you wade through the references.
_________________________
Greg Fretwell

Top
#195760 - 08/20/10 01:50 PM Re: use of sealtite in damp location more than three [Re: gfretwell]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Actually tugging in feeders, considering the bends, will be tougher than you expect. I'd lay on the lube and upsize the raceway one bump. Further, I'd really work on my strapping scheme at every direction change. Lastly, I'd make up my pulling head with extra special care.

You might well consider getting MC - coated? - suitable for exterior use.

If it needs a beauty sheath after the fact that's not so bad. Otherwise, a mere paint job could make the MC blend in. While hefting MC may seem tough, going to Aluminum feeder conductors really cuts weight.
_________________________
Tesla

Top
#195775 - 08/21/10 04:11 PM Re: use of sealtite in damp location more than three [Re: Tesla]
crselectric Offline
Member

Registered: 09/24/06
Posts: 134
Loc: albany, ca
my question was more about fire rating and whether pvc jacketed flex was disallowed in bldg over three floors. So I ended up using steel flex and will have to beautify the exposed portions, the customer doesnt like ropey look, maybe walker duct makes covers I could use.I've seen them used to cover multiple coax runs

Top
#195776 - 08/21/10 06:17 PM Re: use of sealtite in damp location more than three [Re: crselectric]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
I know of no building height limits on LFMC
_________________________
Greg Fretwell

Top