#195757 - 08/20/10 12:55 PM use of sealtite in damp location more than three  
crselectric  Offline
Member
Joined: Sep 2006
Posts: 133
albany, ca
Can I use sealtite in multi family dwelling in outside well covered area to run feeders to third floor, emt would have to be installed in 26 inch sections due to changes in floor framing at stairway decks, its passing thru storage cabinets and floors. original plan was to pass long sections up from basement, but went awry. it would be about 45 foot run, then emt in side apartment.


2017 / 2014 NEC & Related Books and Study Guides

#195758 - 08/20/10 01:58 PM Re: use of sealtite in damp location more than three [Re: crselectric]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
LFMC?
Yes as long as you properly secure it and you can say it is not subject to physical damage.
You also need to pull a grounding conductor in the raceway since it is more than 6'
LFNC "carflex" has similar rules once you wade through the references.


Greg Fretwell

#195760 - 08/20/10 04:50 PM Re: use of sealtite in damp location more than three [Re: gfretwell]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Actually tugging in feeders, considering the bends, will be tougher than you expect. I'd lay on the lube and upsize the raceway one bump. Further, I'd really work on my strapping scheme at every direction change. Lastly, I'd make up my pulling head with extra special care.

You might well consider getting MC - coated? - suitable for exterior use.

If it needs a beauty sheath after the fact that's not so bad. Otherwise, a mere paint job could make the MC blend in. While hefting MC may seem tough, going to Aluminum feeder conductors really cuts weight.


Tesla

#195775 - 08/21/10 07:11 PM Re: use of sealtite in damp location more than three [Re: Tesla]  
crselectric  Offline
Member
Joined: Sep 2006
Posts: 133
albany, ca
my question was more about fire rating and whether pvc jacketed flex was disallowed in bldg over three floors. So I ended up using steel flex and will have to beautify the exposed portions, the customer doesnt like ropey look, maybe walker duct makes covers I could use.I've seen them used to cover multiple coax runs


#195776 - 08/21/10 09:17 PM Re: use of sealtite in damp location more than three [Re: crselectric]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
I know of no building height limits on LFMC


Greg Fretwell