#195179 - 07/14/10 11:20 PM Hot electrical room
wacked Offline
Member
Registered: 12/19/06
Posts: 33
I was wondering if anybody knows what is the acceptable ambient air temperature for an electrical room. I did a check on a facility that I am an FSR for (that has more heat producing devices...transformers etc after a new addition) Much to my horror the temperature was 45 degrees celcius. Apparently when the construction for this new addition is totally complete there will be remediation concerning this hot electrical room.
The CEC talks about ventilation, but does anybody have a firm number or know where I can find????
Top
Tools for Electricians:
#195198 - 07/16/10 09:20 AM Re: Hot electrical room [Re: wacked]
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
that is an interesting problem. Check 6-206 (c) which clearly states 30 degrees. Also 4-004 (8) which calls for conductor derating past 30 degrees. And as you pointed out, 2-318.
Top
#195246 - 07/21/10 03:39 PM Re: Hot electrical room [Re: jay8]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
As Jay states 30 degrees. Hotter, and the equipment must be derated.
Wire is derated per table 5A. 45 C is .85
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals