#194787 - 06/22/10 02:58 PM GFCI Protected Motor, necessary?
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
I was hoping to get some help here, I recently replaced a gfci that was powering a small pump in a tea brewing facility due to the fact that it was always tripping. I assume this problem may be due to the humidity. Someone happened to call OSHA and now they are asking me for a code reference justifying my action. This pump is not with in 6' of water but is near a few tea kettles. Am I in the wrong here, or does it need to be gfci protected?
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
2017 / 2014 NEC & Related Books and Study Guides
#194789 - 06/22/10 03:17 PM Re: GFCI Protected Motor, necessary? [Re: bot540]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Is it in the kitchen?
_________________________
Greg Fretwell
Top
#194790 - 06/22/10 03:29 PM Re: GFCI Protected Motor, necessary? [Re: gfretwell]
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
See, I don't know if it applies. I just read 210.8(B)(2). It is a production room where they brew tea and then bottle it. Technically I would say it is a kitchen. Is there an exception to this being a dedicated piece of equipment?
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
#194792 - 06/22/10 05:10 PM Re: GFCI Protected Motor, necessary? [Re: bot540]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
With a comm kitchen, there are no exceptions for 'dedicated' equipment that is cord & plug connected, 120 volt, etc.

I have to ask, did anyone bother to check the item (pump) that was causing the "trip" on GF? Todays generation of GFI devices usually prevent false tripping.
My experience over many years in comm kitchens, etc. was usually a problem with a plugged in item, and occasionally a 'bad' GF device.

_________________________
John
Top
#194793 - 06/22/10 05:27 PM Re: GFCI Protected Motor, necessary? [Re: HotLine1]
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
Didn't really check the gfi, it was newer and I'm pretty sure they reported the same problem after plugging it into another gfi. The pump is older, maybe something is wrong with it.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
#194794 - 06/22/10 05:31 PM Re: GFCI Protected Motor, necessary? [Re: HotLine1]
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
There does seem to be an interesting interpretation question here. Is the pump in a production area where they brew large quantities, bottle it, ship it out etc. or is it in something like a test kitchen or break area? If the first description is the more accurate, the code doesn't require personnel protection. But determining what a "kitchen" is can be tricky. Is there a set of plans that says its a kitchen? Then its a kitchen. Either way, frankly, if it had GFCI protection previously, it still should.
Top
#194796 - 06/22/10 06:48 PM Re: GFCI Protected Motor, necessary? [Re: Gregtaylor]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Bot:
Based on your above response, I'd be willing to put a Benjamin on the pump motor has an issue. BTW, who asked you for a code reference, the client or the OSHA guys??

_________________________
John
Top
#194797 - 06/22/10 06:53 PM Re: GFCI Protected Motor, necessary? [Re: HotLine1]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The pump problem may be as simple as it is wet inside. Sometime you can fix that by just setting it on the dash of your truck for the day (in the sun).
_________________________
Greg Fretwell
Top
#194810 - 06/23/10 06:45 AM Re: GFCI Protected Motor, necessary? [Re: gfretwell]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
I have seen where OSHA has wanted GFI protection for coffee pots that plug into in a restaurant even though the pot was not in the kitchen. The pots where by the dining area and there was no water around them at all.

P.S. I don't think you want to mess with OSHA they have some pretty hefty fines.
Top
#194828 - 06/24/10 07:54 AM Re: GFCI Protected Motor, necessary? [Re: harold endean]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
The GFI requirements usually pop up where there is water (or potential spillage) present. That's one reason why they are required for kitchen island countertops in dwelling units even if there is no sink in the island (210.8 A 6).
_________________________
Ghost307
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 70 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals