The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
42 minutes 17 seconds ago
Re: Fabricating Guards out of Lexan?
by frank
Today at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Today at 01:26 PM
Why cables look like they do
by Texas_Ranger
Today at 12:33 PM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 20
Webmaster 16
Trumpy 12
ghost307 12
frank 11
Who's Online
1 registered (Webmaster), 0 Guests and 66 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#194781 - 06/22/10 09:44 AM 250.122 [B]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
How are you interpreting “equipment grounding conductors, where installed,” as stated in 250.122[B] when ungrounded conductors are upsized?
Do you consider this as meaning where an EGC is actually pulled in a raceway, or simply where any EGC is present, whether physically pulled or part of a listed cable assembly, such as SER?

It seems that this could possibly be interpreted either way and might allow using an upsized cable assembly containing an equipment-grounding conductor sized only per Table 250.122, as opposed to a raceway where the conductors are pulled and the EGC sized on the ratio of the circular mil area of the upsized ungrounded conductors.
What is your take on this?

TKX

Top
2017 / 2014 NEC & Related Books and Study Guides
#194783 - 06/22/10 10:37 AM Re: 250.122 [B] [Re: KJay]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9060
Loc: Estero,Fl,usa
In a cable, the EGC size gets bigger in proportion to the other conductors getting bigger so 250.122(B) is satisfied.
I assume that is built into the listing standard for all cables.
In the case of SE cable (TYLZ in the white book) it says

Quote:
Based upon tests which have been made involving the maximum heating
that can be produced, an uninsulated conductor employed in a service
cable assembly is considered to have the same current-carrying capacity as
the insulated conductors even though it may be smaller in size.
_________________________
Greg Fretwell

Top
#194784 - 06/22/10 12:58 PM Re: 250.122 [B] [Re: gfretwell]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Thank you Greg. Good find on the SE cable listing.
I had considered that the cables must have had this rule applied already, but now that I have thought this through a bit more, it appears that since Table 250.122 is based on overcurrent, not wire size, it wouldn’t have any relevance when over sizing conductors for things such as voltage drop calcs, being that the actual overcurrent protection would normally be lower than the maximum rating of the conductor.
Unfortunately, sometimes I’m not the sharpest tool in the shed.

Top
#194788 - 06/22/10 03:12 PM Re: 250.122 [B] [Re: KJay]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9060
Loc: Estero,Fl,usa
The white book is a great resource if you are curious about the listing on a particular product. Unfortunately it usually ends up making you want to actually see the listing standard and U/L charges big bucks for that.
I suppose that is why they give the White Book away for free. wink