The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 254 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#194635 - 06/14/10 12:44 PM 6/3 NMWU amperage rating?
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Correct me if I am wrong but since NMWU has a 60 degree rating, then #6NMWU is only good for 55Amps unless it is part of a residential service? (T.2 of the OESC) I am guessing that a sub panel to the garage would not fall under this classification therefore limiting my amperage rating to 55amps and not 60?
_________________________
Never trust an electrician with no eyebrows!!

Top
2014 / 2011 NEC & Related Books and Study Guides
#194641 - 06/14/10 05:06 PM Re: 6/3 NMWU amperage rating? [Re: mr_electrician]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
I think that as long as the Garage is a residential garage and part of a single residential unit, then 60 amps would apply. A residential Garage is not a continuous load and residential services are non continuous loads.
A duplex with a single joint use garage might not qualify.

Talk to the local authority but I think we would allow the greater ampacity as long as the Volt drop does not get rediculous.

Top
#194692 - 06/15/10 10:33 PM Re: 6/3 NMWU amperage rating? [Re: mikesh]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Isn't it a 55 amp feeder fused at 60 amps per Table 13? The differences are that if the load in the garage is greater than 55 amps, the wire is too small; and, the location of the panel in the garage isn't restricted like a residential service.

Top
#197138 - 11/10/10 06:00 PM Re: 6/3 NMWU amperage rating? [Re: twh]
swoop Offline
New Member

Registered: 10/24/10
Posts: 9
Loc: ontario
good luck finding a 55 amp breaker

Top
#197160 - 11/12/10 11:19 AM Re: 6/3 NMWU amperage rating? [Re: swoop]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Twh
Yes you make the most important point. As long as the calculated load is less than 55 amps then the #6 is good and table 13 would allow a 60 amp breaker.

Top