#194635 - 06/14/10 12:44 PM 6/3 NMWU amperage rating?
mr_electrician Offline
Member
Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Correct me if I am wrong but since NMWU has a 60 degree rating, then #6NMWU is only good for 55Amps unless it is part of a residential service? (T.2 of the OESC) I am guessing that a sub panel to the garage would not fall under this classification therefore limiting my amperage rating to 55amps and not 60?
_________________________
Never trust an electrician with no eyebrows!!
Top
Tools for Electricians:
#194641 - 06/14/10 05:06 PM Re: 6/3 NMWU amperage rating? [Re: mr_electrician]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
I think that as long as the Garage is a residential garage and part of a single residential unit, then 60 amps would apply. A residential Garage is not a continuous load and residential services are non continuous loads.
A duplex with a single joint use garage might not qualify.

Talk to the local authority but I think we would allow the greater ampacity as long as the Volt drop does not get rediculous.
Top
#194692 - 06/15/10 10:33 PM Re: 6/3 NMWU amperage rating? [Re: mikesh]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
Isn't it a 55 amp feeder fused at 60 amps per Table 13? The differences are that if the load in the garage is greater than 55 amps, the wire is too small; and, the location of the panel in the garage isn't restricted like a residential service.
Top
#197138 - 11/10/10 06:00 PM Re: 6/3 NMWU amperage rating? [Re: twh]
swoop Offline
New Member
Registered: 10/24/10
Posts: 9
Loc: ontario
good luck finding a 55 amp breaker
Top
#197160 - 11/12/10 11:19 AM Re: 6/3 NMWU amperage rating? [Re: swoop]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Twh
Yes you make the most important point. As long as the calculated load is less than 55 amps then the #6 is good and table 13 would allow a 60 amp breaker.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals