The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 107 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#194629 - 06/14/10 11:59 AM NEC ART 110 working space clearance
Bravo Offline
Member

Registered: 05/04/10
Posts: 30
Loc: NY, USA
I have 2 existing panelboards rated 208/120V 225A that have to be relocated. To minimize cost and shut-down time,
I was going to covert the existing panelboards into junction boxes and pipe feeder and branch circuits to new panleboard location.

Do the new junction boxes have to conform to NEC ART 110.26(A)(1)?

The existing panelboards are mounted to a brick wall, with a new handicapp lift in front of it.

thanks in advance

Top
2014 / 2011 NEC & Related Books and Study Guides
#194631 - 06/14/10 12:10 PM Re: NEC ART 110 working space clearance [Re: Bravo]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Hmmm...with the lift in front, that may be a problem. Boxes have to be accessable.
_________________________
John

Top
#194634 - 06/14/10 12:30 PM Re: NEC ART 110 working space clearance [Re: Bravo]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
Maybe, but 314.29 may still bite you in the butt if that ADA lift is in front of them.

Remember that nowhere in the NEC does it state that the rules can be waived if there is a desire to save money or work quicker.

It's probably best to run it past your AHJ before you hang your hat on it.
_________________________
Ghost307

Top
#194677 - 06/15/10 09:25 PM Re: NEC ART 110 working space clearance [Re: ghost307]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Can you raise or lower the lift and get at the boxes? That way they might not be "readily" accessible, but you are still able to get at them if you move the lift or something like that. Just a thought.

Top
#194691 - 06/15/10 10:19 PM Re: NEC ART 110 working space clearance [Re: harold endean]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The only requirement for "accessible" is you don't have to damage the building finish to get to it. How many J boxes have you worked on that you had to move furniture or crawl on your belly in an attic, all perfectly legal.
_________________________
Greg Fretwell

Top
#194700 - 06/16/10 12:14 PM Re: NEC ART 110 working space clearance [Re: gfretwell]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
Agreed, but take a look at the ADA lift first and make sure that you can even get to the box once it's installed. I've seen a lot of lifts where the support frame is completely solid.
_________________________
Ghost307

Top
#194704 - 06/16/10 12:23 PM Re: NEC ART 110 working space clearance [Re: ghost307]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
I should have added..."checck with your local AHJ" to my original reply.

Not being able to 'see' the situation makes for a tough call.
_________________________
John

Top
#194735 - 06/17/10 06:36 PM Re: NEC ART 110 working space clearance [Re: HotLine1]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
This is definitely a scenario which needs to be verified with the Building Department (any AHJ involved).

Basically, since the existing Panelboards are now Junction Boxes; the need to examine, adjust, service or maintain the Live Circuitry inside is not likely - as compared to a Panelboard, etc.
This, by its self, is open to wide interpretations!

So if the existing "Panelboards-Now Junction Boxes" must comply with 110.26, this will be "Condition 2" - since the ADA Lift assembly is mounted in front of the Junction Boxes.
Condition 2 places 36" minimum between the opening of the J-Box Panelboards, and the closest edge of the ADA Lift.

If the scenario must comply per 110.26 - condition 2, Pullboxes or Wireway Sections mounted above the ADA Lift (or above ceiling, over to a side of the lift, etc.) might be the next best option.

Scott