#194608 - 06/13/10 06:27 PM 3-ways in stairs
romex2121 Offline
New Member
Registered: 06/13/10
Posts: 9
Loc: nm
per the 2008 NEC how many steps need to be present to justify a 3-way system,,, example 2, 4, 6,
Top
Building Codes & Related References
#194611 - 06/13/10 07:23 PM Re: 3-ways in stairs [Re: romex2121]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
210.70 (a)(2)(c) provides the answer...

"(c) Where one or more lighting outlet(s) are installed for interior stairways, there shall be a wall switch at each floor level, and landing level that includes an entryway, to control the lighting outlet(s) where the stairway between floor levels has six risers or more. "
_________________________
John
Top
#194805 - 06/23/10 01:15 AM Re: 3-ways in stairs [Re: HotLine1]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
your local building code may have more to say on the switching requirements
_________________________
"Live Awesome!" - Kevin Carosa
Top
#195137 - 07/13/10 01:08 AM Re: 3-ways in stairs [Re: sparkyinak]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
A lot of what I am seeing these days is not actual switches, but PIR switching on stairwells.
Where as a given flight of stairs might have a sensor on it, it will trigger on movement at the bottom of the stairs and also trigger a delay timer at the top of that set of stairs, that energises the next PIR (and lights) and turns off the lower lighting.
If it saves lights being left on all night,, I'm all for it.

Having said that, in fire situations, it's all lights on.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#195150 - 07/13/10 10:33 AM Re: 3-ways in stairs [Re: Trumpy]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I like motion lights. The light follows you around my house, inside and out.
_________________________
Greg Fretwell
Top
#195425 - 08/02/10 01:06 PM Re: 3-ways in stairs [Re: gfretwell]
Alan Belson Offline
Member
Registered: 03/23/05
Posts: 1803
Loc: Mayenne N. France
My wife follows me round the house switching them off, which is nearly the same but with added mutterings about utility bills laugh ! Seriously, you could lose all the cost saving advantages of low-energy lights if the switch timers are of too short a duration. They don't like short runs.
_________________________
Wood work but can't!
Top
#195427 - 08/02/10 02:46 PM Re: 3-ways in stairs [Re: Alan Belson]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I thought that was true but I have CFLs in the motion lights in my garage, the post light out front and one of the lights inside. They seem to be holding up OK.
_________________________
Greg Fretwell
Top
#200306 - 03/28/11 06:33 AM Re: 3-ways in stairs [Re: romex2121]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Do you really need a 3 way switch at the top and bottom of the stairs when the stairway goes into an attic? smile
Top
#200308 - 03/28/11 06:58 AM Re: 3-ways in stairs [Re: romex2121]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Harold:
It will depend on the definition/use of the 'attic'.

Pull down stairs for access to the space I would say only a switch at the entry, walk-up stairs to a space that could be 'occupied' may require a 3-way. Intent and design fall into the discussion at that point.

_________________________
John
Top
#203286 - 09/18/11 08:02 PM Re: 3-ways in stairs [Re: romex2121]
mikethebull Offline
Member
Registered: 03/18/07
Posts: 100
Loc: Rhode Island
PIR switches are nice but they have to have regular switching. So as not to leave anyone in darkness.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals