The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 12
sparky 10
gfretwell 8
Potseal 7
sparky66wv 6
Who's Online
2 registered (sparky66wv, NORCAL), 251 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#194503 - 06/05/10 08:25 PM Current carrying conductors
ckr1231 Offline
New Member

Registered: 06/05/10
Posts: 5
Loc: Texas
When installing lighting circuits in a raceway from a panel to a contactor cabinet-- Do I have to count switch legs as current carrying conductors? There are 5 277V/20A hots and 5 switch legs and 1 ground in the same raceway. There are no neutral wires in this raceway.
Does this mean the ampacity of the conductors must be derated to 50 percent?
_________________________
There are no bad trips. Only good conductors !!!

Top
2014 / 2011 NEC & Related Books and Study Guides
#194506 - 06/05/10 09:43 PM Re: Current carrying conductors [Re: ckr1231]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I don't really see any way out of it.
_________________________
Greg Fretwell

Top
#194508 - 06/05/10 09:56 PM Re: Current carrying conductors [Re: gfretwell]
ckr1231 Offline
New Member

Registered: 06/05/10
Posts: 5
Loc: Texas
I felt that because they where each the same circuit, I would only be counting 5 current carrying conductors.
_________________________
There are no bad trips. Only good conductors !!!

Top
#194509 - 06/05/10 10:01 PM Re: Current carrying conductors [Re: ckr1231]
ckr1231 Offline
New Member

Registered: 06/05/10
Posts: 5
Loc: Texas
If I can install a raceway not exceeding 24 inches- then I would not have to derate.
That is how I understand the code.
_________________________
There are no bad trips. Only good conductors !!!

Top
#194512 - 06/06/10 01:08 AM Re: Current carrying conductors [Re: ckr1231]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
The issue is the heat dissipated in the wire and it doesn't really matter which circuit they are on.
If "X" amount of current goes down one wire and comes back on another in the same pipe, the accumulated heat is double.

I have heard convincing arguments that when you have several conductors on the same circuit going one way and sharing the available current since they are paralleled you should not need to derate beyond one conductor for each circuit but the language is not there to allow it.
An example would be 10 100w can lights on the same 20a circuit but separate switches on the near end, going through a raceway. As a sanity check, you could only have one neutral coming back but each hot needs to be counted at 20a because that is the size of the O/C device. (11 current carrying conductors).
_________________________
Greg Fretwell

Top
#194514 - 06/06/10 08:21 AM Re: Current carrying conductors [Re: gfretwell]
ckr1231 Offline
New Member

Registered: 06/05/10
Posts: 5
Loc: Texas
Your reply makes perfect sense inregard to the heat being generated. I was not certain if one hot and one switch leg in the same raceway would be considered two current carrying conductors. At this point, my wire is only worth half it's value. I will change it !!

Thank you !!!!
_________________________
There are no bad trips. Only good conductors !!!

Top
#194516 - 06/06/10 11:06 AM Re: Current carrying conductors [Re: ckr1231]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Just remember you can use the 90c column for THHN so on a 20a breaker you can use #10 at 50%.
It might even end up cheaper to run another raceway and split them up. Be sure you correctly pair them
_________________________
Greg Fretwell

Top
#194518 - 06/06/10 05:51 PM Re: Current carrying conductors [Re: gfretwell]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Realisticly you'll need a 1" pipe and #10 THHN/THWN-2/MTW...

The Code does not provide field electricians with an 'out' such that they can rejigger standards based upon their opinion or calculations.

That from time to time something is over engineered is balanced against the reality of the hazard of under engineering.

BTW, W a y back in the day -- everyone thought that if it worked it was safe. Then electrical fires were invented...

And the NEC was born.
_________________________
Tesla

Top
#194520 - 06/06/10 08:07 PM Re: Current carrying conductors [Re: Tesla]
ckr1231 Offline
New Member

Registered: 06/05/10
Posts: 5
Loc: Texas
This is a 3/4 conduit (EMT) about 26 inches long. Each circuit is drawing about 7 to 8 amps. This was done during a shut-down. I found it after the fact.
_________________________
There are no bad trips. Only good conductors !!!

Top