The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Search Function
by Webmaster
01/18/17 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 09:17 PM
ESA Arc flash course
by frank
01/18/17 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
gfretwell 12
Trumpy 12
Who's Online
1 registered (gfretwell), 0 Guests and 182 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#194454 - 06/03/10 12:23 PM Clearance over roof
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I don't have a 2008 code available, only 2005. In the 2005 it says the clearance for service drops over a roof area is 8ft., with an exception of 3 feet where the roof pitch is 4 inches in 12 inches. Is this the same in the 2008 code? Thanks for the reply..

Top
2017 / 2014 NEC & Related Books and Study Guides
#194457 - 06/03/10 04:38 PM Re: Clearance over roof [Re: sparkync]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Presuming that the voltage between conductors does not exceed 300 volts, 3 feet is still OK.
_________________________
Few things are harder to put up with than the annoyance of a good example.