The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 263 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#194391 - 05/28/10 11:10 PM 3 phase on triplex
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
Correct me if I'm wrong in my thinking, please. I have a customer that currently has 3 seperate runs of 4/0 URD triplex. Each run is in its own Sch 40 PVC pipe. They travel 175 feet underground from the main service to a control building. One of the triplex runs are feeding a 200 amp(120/240)single phase panel. The other two are paralleled into a 400 amp disconnect feeding a phase converter.

My dilemma is, I am removing phase converter and installing true 3 phase service (120/240). Can this be done(rightfully) with the 3 runs. My thinking is to use all 3 runs to feed 400 amp switch. Can I parallel these 3 runs in the following manner?

Run #1: A,B,N
Run #2: B,C,N
Run #3: C,A,N

I would then run a new service to the single phase panel. Or should I just bite the bullet and start over with quadraplex?

Thanks, Merlin

Top
2014 / 2011 NEC & Related Books and Study Guides
#194398 - 05/30/10 03:47 AM Re: 3 phase on triplex [Re: Merlin]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Your transformer taps from the utility tell the tale.

Just what phases are available?

You just can't assume anything.
_________________________
Tesla

Top
#194399 - 05/30/10 01:38 PM Re: 3 phase on triplex [Re: Merlin]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
Presuming that the POCO can give you three phase, I'd say that you would have to replace the wire. Each of the 3 neutrals that in parallel will carry 1/3 third of the unbalanced portion of the total. This could introduce counter electromotive force CEMF or impedece in the triplex.

A good way to look at it in an extreme condition example. 100 amps on any one phase would put 50 amps on it's respective phase in only two of the triplexes and 33 amps on each of the three triplex neutrals. Another way to look at it is that 100 amps between two phase will have one of the triplex balanced while the other two triplexes will be severely unbalanced.

Each of the unbalance triplexes will generate a megnetic field around them and impede current flow. Worse case, something in the triplexes can burn up. The only way your proposed plan would work if there was an even load on all three phases all the time. That is why it is very important to have all the conductors of a circuit in the same raceway.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#194439 - 06/02/10 03:08 PM Re: 3 phase on triplex [Re: sparkyinak]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
In duct you have to have all 4 wires in each raceway and possibly a bonding conductor too.

Top
#194446 - 06/02/10 08:21 PM Re: 3 phase on triplex [Re: mikesh]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
IMHO, I would 'bite the bullet'!
_________________________
John

Top
#194485 - 06/04/10 09:16 PM Re: 3 phase on triplex [Re: HotLine1]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Have you done a neutral load calc?
I'm just wondering if those triplex URD with reduced neutrals might possibly be a problem on a 3-phase system with multiple single-phase loads.
You said 120/240 3-phase, but is that correct?