#194159 - 05/13/10 01:41 PM Article 310.15.(B)(2)(c)
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
How is Article 310.15.(B)(2)(c) applied in your area? What is used for a base temperature? Can one use the information on the weather channel for your area's average temperature on the hottest month of the year? Do you have to use the ASHRAE Handbook? How about that 3 questions for the price of one smile
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#194163 - 05/13/10 03:29 PM Re: Article 310.15.(B)(2)(c) [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I cross posted this over on Fl IAEA to see what they say.

I never had an inspection on a roof since this article appeared.
_________________________
Greg Fretwell
Top
#194166 - 05/13/10 04:06 PM Re: Article 310.15.(B)(2)(c) [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Thanks Greg, since I live in a northern state, we don't have much of an issue with this type of installation but I'm sure you might or possibly some other state.
_________________________
George Little
Top
#194179 - 05/14/10 10:12 AM Re: Article 310.15.(B)(2)(c) [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I got this back From Bryan Holland (BHGravity here)
Quote:

I am using the guidelines established by the CDA. As indicated in the FPN, the CDA guidelines utilize the average of the 2% ASHRAE design temperatures for each region and major city in the state.

The guildelines and sliding scale card can be obtained FREE from www.copper.org
_________________________
Bryan P. Holland, ICC Electrical Code Official
CBO, Plans Examiner, Inspector, Instructor
Secretary - IAEI Florida Gulf Coast Division
Secretary - BOAF Gulf Coast Chapter




_________________________
Greg Fretwell
Top
#194195 - 05/14/10 08:13 PM Re: Article 310.15.(B)(2)(c) [Re: gfretwell]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
_________________________
Greg Fretwell
Top
#194228 - 05/16/10 07:13 PM Re: Article 310.15.(B)(2)(c) [Re: gfretwell]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
In Las Vegas the local ordinances super-cede this Code provision.

Ground temperatures are considered such a threat that the typical PVC-under-slab run is restricted to absolute minimums and the conductors get derated.

Hence, a grocery store ( example ) has all of its circuits run in EMT overhead and de-rated one bump.

_________________________
Tesla
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (sparkyinak), 108 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals