The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 202 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#194159 - 05/13/10 01:41 PM Article 310.15.(B)(2)(c)
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
How is Article 310.15.(B)(2)(c) applied in your area? What is used for a base temperature? Can one use the information on the weather channel for your area's average temperature on the hottest month of the year? Do you have to use the ASHRAE Handbook? How about that 3 questions for the price of one smile
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#194163 - 05/13/10 03:29 PM Re: Article 310.15.(B)(2)(c) [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I cross posted this over on Fl IAEA to see what they say.

I never had an inspection on a roof since this article appeared.
_________________________
Greg Fretwell

Top
#194166 - 05/13/10 04:06 PM Re: Article 310.15.(B)(2)(c) [Re: gfretwell]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Thanks Greg, since I live in a northern state, we don't have much of an issue with this type of installation but I'm sure you might or possibly some other state.
_________________________
George Little

Top
#194179 - 05/14/10 10:12 AM Re: Article 310.15.(B)(2)(c) [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I got this back From Bryan Holland (BHGravity here)
Quote:

I am using the guidelines established by the CDA. As indicated in the FPN, the CDA guidelines utilize the average of the 2% ASHRAE design temperatures for each region and major city in the state.

The guildelines and sliding scale card can be obtained FREE from www.copper.org
_________________________
Bryan P. Holland, ICC Electrical Code Official
CBO, Plans Examiner, Inspector, Instructor
Secretary - IAEI Florida Gulf Coast Division
Secretary - BOAF Gulf Coast Chapter




_________________________
Greg Fretwell

Top
#194195 - 05/14/10 08:13 PM Re: Article 310.15.(B)(2)(c) [Re: gfretwell]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
_________________________
Greg Fretwell

Top
#194228 - 05/16/10 07:13 PM Re: Article 310.15.(B)(2)(c) [Re: gfretwell]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
In Las Vegas the local ordinances super-cede this Code provision.

Ground temperatures are considered such a threat that the typical PVC-under-slab run is restricted to absolute minimums and the conductors get derated.

Hence, a grocery store ( example ) has all of its circuits run in EMT overhead and de-rated one bump.
_________________________