The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
52 minutes 53 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#193964 - 05/01/10 07:36 PM Sizing contactors for transformer loads
bigpapa Offline
Member

Registered: 03/18/06
Posts: 77
Loc: canada
How do you size a contactor that is in the primary circuit of a transformer?
I am looking for a specific CEC rule or guidance.
In this case 75KVA 600V 3PH primary with upstream 70A circuit breaker.

I know you can use definite purpose contactors but i think you have to upsize them for inductive loads. If that is the case, does the code address this specifically?

Top
2014 / 2011 NEC & Related Books and Study Guides
#193967 - 05/02/10 10:46 AM Re: Sizing contactors for transformer loads [Re: bigpapa]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
2008 NEC Article 450 450.3 (B).
See Table 450.3(B).
The way I usually do it (if no charts handy).
480 primary/120-208 secondary.
480x1.73 = 830.4 round out to 830
208 x 1.73 = 359.84 round out to 360
75 x 1000 = 75000 Divided by 830 = 90.36 amp pri.
7500 divided by 360 = 208.33
Pri can be up to 250% if seconday protected no more then 125%
So 70 amp breaker Pri. Fine
Secondary 125% x 208.33 = 260.4 amps
See (450.3 (B) Table note 1.
Then go to 240.6.
Thats the way I;ve done it.
Yoopesup

Top
#193969 - 05/02/10 09:54 PM Re: Sizing contactors for transformer loads [Re: Yoopersup]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
I don't see a rule about controlling transformers, so 14-400 should cover it.
Quote:
14-400 Control devices shall have ratings suitable for the connected load of the circuits that they control and, with the exception of isolating switches, shall be capable of safely establishing and interrupting such loads
I wouldn't think the transformer is the load. Rather, it has a load. If you connect only capacitors to the transformer, doesn't the primary have a leading power factor like a capacitor and not a lagging power factor like a motor?