#193952 - 04/30/10 10:03 PM Wye Delta Start Closed Transition
DYNAMITE Offline
Member
Registered: 12/22/03
Posts: 36
Loc: Winkler, MB, Canada
Would anyone know how to size the resistors on a Wye start/delta run closed transition starter? Say for a 50 Hp 230V motor?
Top
Tools for Electricians:
#194021 - 05/05/10 01:48 AM Re: Wye Delta Start Closed Transition [Re: DYNAMITE]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
I believe the Resistors would be sized ("size" = Resistance value - in Ohms), so as to allow the same level of Current that the "Wye" configuration does.

Example:
Motor's FLA = 130 Amps
Starting (Wye Connection) Ampere = +/- 75 Amps
Resistors are sized to allow +/- 75 Amps at rated Voltage.

I am not 100% sure on this, so let me find some references, then reply back.

Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#194026 - 05/05/10 08:54 AM Re: Wye Delta Start Closed Transition [Re: Scott35]
DYNAMITE Offline
Member
Registered: 12/22/03
Posts: 36
Loc: Winkler, MB, Canada
That makes sense to me. The smaller you make them the closer to normal current you have. The next question is Watt ratings. The resistors are only in the circuit for a split second in the transition between wye and delta so would you need full power ratings(Peak I^2 R) on them?
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals