The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
1 registered (Radar), 249 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#193839 - 04/22/10 10:42 AM Box size?
sparky806 Offline
Member

Registered: 12/07/02
Posts: 59
Loc: Shawnee, KS, USA
Hello everybody. I left my NEC at home and need to size a pull box ASAP. I will have 12(twelve) 3 1/2 inch emt's in and 12 out. Each will have 4 500mcm and 1 1/0. All conductors will make a 90 degree turn in this box. Thanks in advance, Richard

Top
2014 / 2011 NEC & Related Books and Study Guides
#193840 - 04/22/10 03:28 PM Re: Box size? [Re: sparky806]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
2008 NEC 314.28 (2)
6x3.5 = 21
11 x 3.5 = 38.5

21 + 38.5 = (59.5 x 59.5 X 6 Min.)
figured that there all in a row both walls.


Edited by Yoopersup (04/22/10 03:29 PM)

Top
#193844 - 04/22/10 08:29 PM Re: Box size? [Re: Yoopersup]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Adding to what Yooper said, make sure that the raceways containing the same conductors ie; Raceway "A" has conductors coming into the pull box and Raceway "B" has these conductors going out are at least 21 inches apart.
_________________________
George Little

Top
#193847 - 04/22/10 09:34 PM Re: Box size? [Re: George Little]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Yep 6 x 3.5 = 21 inches .

Top
#193850 - 04/23/10 03:00 AM Re: Box size? [Re: Yoopersup]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
12 in and 12 out...

Where do you get 6 x 3.5" ?

Right off the bat the bonding run is too small...IF this is one load.

It must be sized to handle the fault current for ALL hot conductors at the SAME INSTANT.

Are you really running 12 x 500kCMIL x 3 hots and 1 neutral?

Or is this a bank of runs to dependent panels off of a bank of independent breakers?

BTW your neutral seems massively oversized -- IF you're driving mainly 3-phase loads.

What does the EE have on his 1-line? Sounds like he goofed.

At these power levels bus-duct or cable-bus (MPHusky) is normally used.

Is this a high-rise building?...

Can you use cable-tray and MC?...

Too many unknowns to take a stab at.

I can say, twelve feeders flat across is a monster rack and ordinary strut is going to sag. You'll need double deeps.

Further, during the pull operations -- don't spare the lube.


Edited by Tesla (04/23/10 03:08 AM)
_________________________
Tesla

Top
#193851 - 04/23/10 06:51 AM Re: Box size? [Re: Tesla]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
the six comes from 314.28 (2) Angle ,U pills, Or splices.
The distance between raceways enclosing the conductors shall not be less then SIX TIMES the metric designator (Trade size) of the larger raceway.
I don't recall a Question about the ampacity ??? This could be 12 - 400 amp feeders for all we know.

Top
#193861 - 04/23/10 07:41 PM Re: Box size? [Re: Yoopersup]
sparky806 Offline
Member

Registered: 12/07/02
Posts: 59
Loc: Shawnee, KS, USA
First of all I want to say thanks for everyones input. What I am doing is refeeding a 475' piece of 3000amp busduct. The Ideal way would be to extend the duct, however it was installed in 1951 and I have not been able to find matching duct.
I wouldn't really call this a high rise. It's 5 stories, 1.5 million square feet. Complete rehab. All switch gear and bus duct is original. We have redone the risers and panels on parts of 3 floors. The building had it's own generators when built. We removed those and tied it into POCO's grid last year. If anyone knows where to get about 100 feet of 50 year old Westinghouse 3000amp bus duct, then I won't need that pull box.

Top
#193862 - 04/23/10 09:15 PM Re: Box size? [Re: sparky806]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Just Curious how you came up needing 12- sets of 500Kcmil??
& the 1/0 in each pipe ain't gonna do it? (250.122(C)
& Teslas Right Neutral seems kinda Big?? (prally mostly 3 phase loads).

Top
#193863 - 04/24/10 12:19 AM Re: Box size? [Re: Yoopersup]
homer Offline
Member

Registered: 09/30/04
Posts: 68
Loc: Vancouver, WA, USA
Sparky,
One way of solving your problem is to install any type of new 3000 amp busway from the source to a point close to the terminal cabinet of the old busway. Install a terminal cabinet on the new busway and a set of short conduit nipples to the old busway terminal cabinet. Install 500kcmil (or smaller parallel) jumpers from new to old. You will be tens of thousands of dollars ahead of the game. Materials may be more expensive, labor will be way less!!!
Homer

Top
#193864 - 04/24/10 12:47 AM Re: Box size? [Re: homer]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Google Salinger, they have an amazing amount of old bus-duct.


www.salingerelectric.com
_________________________
Tesla

Top