#193792 - 04/19/10 10:50 PM feeder sizing
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
how should I calculate generator feeders? I have a 17 KW generator 71 amps, 310.15 allows #4 for 100 amps, but does it allow #6 for 71 amps? Do I size according to 310.16 which is still #4?
Thanks,
H20
Top
2017 / 2014 NEC & Related Books and Study Guides
#193795 - 04/20/10 12:32 AM Re: feeder sizing [Re: watersparkfalls]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You can only use 310.15(B)(6) if this is a main feeder for the entire dwelling, basically an extension of the service entrance from a disconnect. That is, by definition, a #4 minimum. In no case could you interpolate down to a #6.
Any other application has to use 310.16.
_________________________
Greg Fretwell
Top
#193802 - 04/20/10 09:46 AM Re: feeder sizing [Re: gfretwell]
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
thanks Gfretwell
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals