#193710 - 04/14/10 08:56 PM Dedicated Work Space
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
The Space located 6'above Panels, Services, Motor Control centers, and Distribution Equipment and as wide as the Equipment is solely for the Electrician, right? No piping or other ducts etc. are allowed in this space. Does the 6'rule (110.26) also apply to disconnects, or are they exempt from the rule? Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#193717 - 04/15/10 09:47 AM Re: Dedicated Work Space [Re: SJT]
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
It depends. Check 110.26 (E)
_________________________
Alan--
If it was easy, anyone could do it.
Top
#193719 - 04/15/10 11:57 AM Re: Dedicated Work Space [Re: Alan Nadon]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
You also have the issue of dedicated electrical space above the 6'6 working space.

Quote:
(1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (F)(1)(d).
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
(b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
(c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.
(d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling.
_________________________
Greg Fretwell
Top
#193735 - 04/16/10 10:03 AM Re: Dedicated Work Space [Re: gfretwell]
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
110.26(E) applies ONLY to service equipment, switchboards, panelboards, or motor control centers.
Does the disconnect function as one of those items ?
Yes or no, determines if the rule applies, i.e. it depends.
_________________________
Alan--
If it was easy, anyone could do it.
Top
#193738 - 04/17/10 12:09 AM Re: Dedicated Work Space [Re: Alan Nadon]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
That is always the question. When do you apply "working space" to disconnects? and the answer seems to be which disconnect and what AHJ are you talking to.
_________________________
Greg Fretwell
Top
#193836 - 04/21/10 08:30 PM Re: Dedicated Work Space [Re: gfretwell]
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
It can get crowded out there in a Mechanical room, between the plumbers pipes, HVAC guys, and technicians. It's good those clearance rules out there. It's almost like picturing an invisible 3D frame over your Equipment and claiming that territory.
Top
#193842 - 04/22/10 08:15 PM Re: Dedicated Work Space [Re: SJT]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
I'd say fuseable disconnects & controllers come into that because you can change the fuses while engerized.
Top
#193891 - 04/26/10 10:51 AM Re: Dedicated Work Space [Re: Yoopersup]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
I always though that an HVAC disconnect(disco) would need work space clearances (WSC) because they have to be serviced. Now the Dep. of Community Affairs tell me that the HVAC disco does not need WSC because it is not "serviceable equipment". I said, OK maybe that would be so if there are no fuses, but I believe if there are fuses, you need WSC. That would be the way I call it if I see it.
Top
#193894 - 04/26/10 04:34 PM Re: Dedicated Work Space [Re: harold endean]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
The way it has been explained to me is that a HVAC service tech might need to test the voltage on the line side of the disconnect. I could make that argument for every switch in the house.

Most fused disconnects (all?) have the fuse on the load side of the disconnect so nobody should need to handle an energized fuse.
_________________________
Greg Fretwell
Top
#193895 - 04/26/10 06:08 PM Re: Dedicated Work Space [Re: gfretwell]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
If you read 110.26 (a) Fused disconnects & Controllers (changing heaters ect )come under it. If you read in the handbook (I know its not the code) explaination it covers thoses items.
just my call.


Edited by Yoopersup (04/26/10 06:08 PM)
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals