I have a piece of commercial kitchen equipment that requires 2 120 volt circuits. Each pulls 1750 watts. Is there anything wrong with pulling 12/3 mc cable with a common neutral to this equipment, provided I put a double pole breaker on the circuit? Thanks...
Top
Work Gear for Electricians and the Trades
#193645 - 04/12/10 07:07 AM Re: Common neutral question [Re: sparkync]
Rewire Offline
Member
Registered: 02/23/08
Posts: 165
Loc: Missouri
How is the connection made to the equipment?Unless the manufacturer says don't I see no NEC issue with the what you want to do.
Top
#193648 - 04/12/10 08:35 AM Re: Common neutral question [Re: Rewire]
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
The equipment plugs directly into a regular 120 volt outlet. They will both probably be used at the same time.
Thanks..
Top
#193650 - 04/12/10 08:51 AM Re: Common neutral question [Re: sparkync]
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
I see no problem at all. Even if only one of the items is used, the neutral will carry 100% of the load. If both are used, then the current will be equally divided among the hot legs with the neutral carrying any imbalance.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#193709 - 04/14/10 08:23 PM Re: Common neutral question [Re: EV607797]
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
I am not a big fan of common neutrals. If one circuit is overloaded for whatever reason, it also takes out the other circuit, being it's on a 2 pole breaker. I would stay with a neutral for each circuit, especially kitchen equipment.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals