The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
49 minutes 28 seconds ago
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 252 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#193490 - 04/05/10 06:15 AM transformer above ceiling?
cgw Offline

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
30KVA dry type transformer (480 X 120/208)
Can it be located above a suspended accessible ceiling (say in a medical office building)?
Can it be located above this ceiling if the ceiling space is a return air plenum?

2014 / 2011 NEC & Related Books and Study Guides
#193502 - 04/05/10 04:10 PM Re: transformer above ceiling? [Re: cgw]
Gregtaylor Offline

Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
NEC 2008 450.13(B) says, generally for this size and type, you can. The plenum space question is not addressed.

#193506 - 04/05/10 06:40 PM Re: transformer above ceiling? [Re: Gregtaylor]
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
300.22 (c)(2) should be read, and then I suggest you speak to the local AHJ for his/her interp. Under 50 KVA is no issue, BUT...the air handling ceiling needs to be addressed. Also, you may want to have a cut sheet for the exact xfr you intend to install.

#193508 - 04/05/10 07:52 PM Re: transformer above ceiling? [Re: HotLine1]
gfretwell Offline


Registered: 07/20/04
Posts: 9025
Loc: Estero,Fl,usa
I think this is probably legal, depending on the transformer but it might be a questionable design choice. If that transformer smokes it will share the joy with the rest of the building pretty fast, at least that HVAC zone anyway.
Greg Fretwell

#193588 - 04/08/10 05:07 PM Re: transformer above ceiling? [Re: gfretwell]
Tesla Offline

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
If the Life Safety System ( Fire Alarm ) is up to snuff a duct detector is going to shut things down well enough in time.

Not quite the same set-up...

But I rigged a 45kVA XFRMR, dry-type, above a grid to give isolated power to data loads. Upon the detection of fire, within this space only, a shunt-trip killed total power - with a time delay of seconds so that the data state could be frozen/ preserved. Subsequently the dry fire system would be flooded into the now unpowered space.

So the question of plenum return air really would seem to be a life safety question not to be answered within our Code.