#193117 - 03/19/10 05:59 AM Transformers & Feeders: 3 Phase 4 Wire Wye
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA

Transformers & Feeders: 3 Phase 4 Wire Wye


Five Drawings of Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus OCPDs and Panelboards for:
3 Phase 4 Wire Wye Transformers
(Two Voltage SDS)
NOTE: Click on Image to view Full-Sized Image

----------------------------------------------------------

Drawing 3PH4WY-1: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary OCPD at Panelboard.


-----------------------------------------------------------

Drawing 3PH4WY-2: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders, Additional Panelboard "Subfed".
Secondary OCPD at First Panelboard.


-----------------------------------------------------------

Drawing 3PH4WY-3: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Two Panelboards fed via Tapped Feeder.
Secondary OCPD at each Panelboard.


-----------------------------------------------------------

Drawing 3PH4WY-4: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Two separate Panelboards fed by Secondary Feeders- each set derived from "X" Terminals.
Secondary OCPD at each Panelboard.


-----------------------------------------------------------

Drawing 3PH4WY-5: 480V x 208Y/120V 3 Phase 4 Wire Wye - Star Point Grounded Neutral
(Max. Voltage To Ground = 120V; With Grounded Conductor)
Distribution Panel fed by Secondary Feeders.
With Secondary OCPD at Distribution Panel.


-----------------------------------------------------------

Text #3: Two Voltage SDS - Primary & Secondary OCPDs
(Click on Image to view Full-Sized Image)


-----------------------------------------------------------
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals