Transformers & Feeders: 3 Phase 3 Wire Wye

Five Drawings of Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus OCPDs and Panelboards for:
3 Phase 3 Wire Wye Transformers
(Single Voltage SDS)
NOTE: Click on Image to view Full-Sized Image

-------------------------------------------------------------

Drawing 3PH3WY-1: 480V x 208V 3 Phase 3 Wire Wye - Star Point Grounded
(Max. Voltage To Ground = 120V; no Grounded Conductor)
Single Panelboard fed by Secondary Feeders:
No Secondary OCPD (Secondary Feeders Protected by Primary OCPD).


-------------------------------------------------------------

Drawing 3PH3WY-2: 480V x 208V 3 Phase 3 Wire Wye - Star Point Grounded
(Max. Voltage To Ground = 120V; no Grounded Conductor)
Single Panelboard fed by Secondary Feeders:
With Secondary OCPD at Panelboard.


-------------------------------------------------------------

Drawing 3PH3WY-3: 480V x 208V 3 Phase 3 Wire Wye - Star Point Grounded
(Max. Voltage To Ground = 120V; no Grounded Conductor)
Two Panelboards fed via Tapped Feeder:
With Secondary OCPD at each Panelboard.


-------------------------------------------------------------

Drawing 3PH3WY-4: 480V x 208V 3 Phase 3 Wire Wye - Star Point Grounded
(Max. Voltage To Ground = 120V; no Grounded Conductor)
Two separate Panelboards fed by Secondary Feeders- each set derived from "X" Terminals.
No Secondary OCPD (Secondary Feeders Protected by Primary OCPD).


-------------------------------------------------------------

Drawing 3PH3WY-5: 480V x 208V 3 Phase 3 Wire Wye - Star Point Grounded
(Max. Voltage To Ground = 120V; no Grounded Conductor)
Distribution Panel fed by Secondary Feeders. No Main OCPD at Distribution Panel
(Secondary Feeders Protected by Primary OCPD).


-------------------------------------------------------------

Text #1: Single Voltage SDS - Primary & Secondary OCPDs
(Click on Image to view Full-Sized Image)


------------------------------------------------------------

Text #2: Single Voltage SDS - Primary OCPD ONLY
(Click on Image to view Full-Sized Image)



-----------------------------------------------------------------------------------------
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 49 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals