#193114 - 03/19/10 05:33 AM Transformers & Feeders:3Ph 3W Closed Delta
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA

Transformers & Feeders:3Ph 3W Closed Delta 1/2

First Set of Drawings for 3 Phase 3 Wire Closed Delta Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus Primary OCPDs and Panelboards
(Single Voltage SDS, Primary & Secondary OCPD)
NOTE: Click on Image to view Full-Sized Image

Drawing 3PH3W-CD1A_PS_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Center Tap Grounded
(Max. Voltage To Ground = 200V, Nominal = 120V; no Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Secondary OCPD at Panelboard.


----------------------------------------------------

Drawing 3PH3W-CD2A_PS_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Corner Grounded
(Max. Voltage To Ground = 240V, Phase "B" = Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Secondary OCPD at Panelboard.


---------------------------------------------------

Drawing 3PH3W-CD3A_PS_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Ungrounded
(Max. Voltage To Ground = 0V, no Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Secondary OCPD at Panelboard.


-------------------------------------------------------------

Text #1: Single Voltage SDS - Primary & Secondary OCPDs
(Click on Image to view Full-Sized Image)



-------------------------------------------------------------
-------------------------------------------------------------
-------------------------------------------------------------


Transformers & Feeders:3Ph 3W Closed Delta 2/2

Second Set of Drawings for 3 Phase 3 Wire Closed Delta Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus Primary OCPDs and Panelboards
(Single Voltage SDS, Primary OCPD Only)
NOTE: Click on Image to view Full-Sized Image

-----------------------------------------------------

Drawing 3PH3W-CD1B_PRI_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Center Tap Grounded
(Max. Voltage To Ground = 200V, Nominal = 120V; no Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Primary OCPD.


-----------------------------------------------------

Drawing 3PH3W-CD2B_PRI_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Corner Grounded
(Max. Voltage To Ground = 240V, Phase "B" = Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Primary OCPD.


-----------------------------------------------------

Drawing 3PH3W-CD3B_PRI_OCPD: 480V x 240V 3 Phase 3 Wire Closed Delta; Ungrounded
(Max. Voltage To Ground = 0V, no Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
Secondary Feeders Protected by Primary OCPD.


------------------------------------------------------------

Text #2: Single Voltage SDS - Primary OCPD ONLY
(Click on Image to view Full-Sized Image)
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals