The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 216 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#19306 - 12/24/02 02:48 AM One more generator question??
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Anyone see anything wrong with putting bigger load in a generator panel than the generator is capable of carrying,(as long as the individual circuits are protected and the inter-locks are in place for the mains, and the panel is rated for the combined load, etc....etc.....)so that the individual loads can be turned on and off as needed??? For example....say you've got your well pump on and a few lights and receptacles, and you want to heat your water up, so you turn your lights or whatever off, and turn your water heater on... Am I missing something in the code.. Seems like this should be OK since, if the generator gets overloaded, it will shut down anyway??? Thanks again for the input..I want to make sure I got everything right..I've got a couple of these jobs coming up......... Steve

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#19307 - 12/24/02 03:41 AM Re: One more generator question??
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
In my experience, it's a good idea to have the customer participate in sizing the critical loads.

Trying to keep it simple , i usually ask that they add up this in wattage x 1.25%

However, when they realize the $$$ involved in higher KW genny's the issue of 'juggling always arises.

There are many undesized genny's that have an all inclusive auto-T switch , simply surviving on a crap shoot re; loads on @ time of transfere.

This, as opposed to the Gen-Tran 20216 or similar models that require manual intervention probably buys one little 'code' slack, yet makes 'juggling' loads a practical option.

Top
#19308 - 12/28/02 06:11 PM Re: One more generator question??
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Sparkynyc,
Do you guys, not have Maximum Demand Calculations, in the US?.
These give the fact,(called Diversity Factor),that not all of the loads will be drawing current at the same time.
We use these calcs, to size Mains and Sub-Mains, over here in New Zealand.
These Calcs, can also be applied to Gen-Sets
too, as they are the same as a Mains supply.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#19309 - 12/29/02 12:10 AM Re: One more generator question??
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
The power companies use a derating factor from the calculated load of a building. This allows them to use smaller service wire than the calculated load would require if wired by the NEC. They know that electrical usage is not what the calculated load is. Different occupancies have different derating factors depending on simular loads served and thier usage history.
Check with the local utility and the AHJ before sizing the generator. Also find out from your customer what he really wants from the generator. You may be suprised how small the required generator will be. Of course if the customer has plans to add load later that should be addressed.
Good luck
_________________________
ed

Top