The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 229 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#193031 - 03/16/10 11:55 AM Health Care Facility
ggardiner Offline

Registered: 10/22/01
Posts: 81
Loc: Calgary, Alberta Canada
First off let me say it has been over 15 years since I was involved in anything using conventional electrical components in Canada and maybe 20 years since I was ever asked anything to do with Health Care Facitlies in Canada.
In the US there is cable specified for Health Care (AC-HFC) and for non Heath care MC is used. Now there is a crossover between the two. In Canada I had the impression normally for normal 120 receptalces we would use the hospital grade receptacle and 12/2 BX with insulated ground is this correct or am I in need of a refesher on Canadain Standards?

2014 / 2011 NEC & Related Books and Study Guides
#193056 - 03/17/10 11:56 AM Re: Health Care Facility [Re: ggardiner]
mikesh Offline

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
It depends.
The use of armoured cable requires approval from the local authority. IE special permission.
Locally that is very easy to get. The bonding conductor is required to be insulated against accidental contact with the armour if you are using armoured cable (BX) or (AC)
Typically that is ISO (isolated) the construction of ISO bx is insulated power conductors and 1 insulated bonding conductor as well as a bare. Regular AC cable is not permitted as the bonding wires are bare and it is not a #12 as is the minimum size for the insulated bonding wire.
Teck cable sized for the minimum #12 bonding wire is acceptable and in combustible buildings we even permit 10-2 loomex as the bonding wire is #12. Clearly the voltage drop and potential rise test have to be passed and the results submitted to the inspection department.
If you are doing a real hospital as opposed to a GP's office you will be using pipe and wire.

#193074 - 03/18/10 09:11 AM Re: Health Care Facility [Re: mikesh]
ggardiner Offline

Registered: 10/22/01
Posts: 81
Loc: Calgary, Alberta Canada